    I am connecting to a 200 amp service panel and 300' to a 100 amp sub panel. #4 or #2
    I am connecting to a 200 amp service panel and running 300 ft to a 100 amp sub panel. At the 100 amp sub panel it will be running mostly lights and a occasional small appliance. Do I need to use #2 for the hot leads or can I get by with #4 ?
  • Apr 10, 2014, 11:25 AM
    donf
    Before you start trenching, can your main service panel accept a 100 breaker?

    Next issue, if go from the main service panel to a downstream panelboard, you must use a 4 wire feed.

    Next, to deliver 240 volts - 100 amps a distance of 300' will require 2/0 AWG copper conductors. For Aluminum, you would need 4/0 conductors.

    That's allowing for a 3% Voltage drop. The recommended allowance is 5% end to end (feeder and branch circuit).
  • Apr 11, 2014, 05:58 AM
    ixoye55
    Quote:

    Originally Posted by donf View Post
    Before you start trenching, can your main service panel accept a 100 breaker?

    Next issue, if go from the main service panel to a downstream panelboard, you must use a 4 wire feed.

    Next, to deliver 240 volts - 100 amps a distance of 300' will require 2/0 AWG copper conductors. For Aluminum, you would need 4/0 conductors.

    That's allowing for a 3% Voltage drop. The recommended allowance is 5% end to end (feeder and branch circuit).