    Oil furnace - no pressure and temp drops below minimum
    I have an intermittent problem with my oil furnace. It is a hot water baseboard system. Here are the symptoms:
    1. Call for heat from a thermostat in a heating zone
    2. There is a sound of air in pipes and boiler down to 80'F and not firing but circulation is occurring and zones are not getting up to temp.
    3. No water pressure in boiler when cold (80 degrees Fahrenheit).
    4. Burner didn't fire until down to 80 degrees Fahrenheit, even though the min and max temps on the Honeywell Strip Gauge are set to 140 and 180'F (see attached picture).
    5. Pressing the reset on the Honeywell R8184 unit on top of the motor did nothing (see pic), I didn't know about the one on the side of the motor at that time.
    6. After the boiler fired, the pressure increased to about 15psi and a few drops of water dripped out of the vent above the Extrol 30 expansion tank but stopped quickly. (See attached picture)
    7. Boiler temp went up to 212 degrees Fahrenheit before turning off.
    8. Extrol pressure measured 12psi while hot water was circulating through a zone. A few drops of water came out of the bottom of the extrol but it is not full of water under the diaphragm (top half of the tank is hot, bottom half is room temperature). When it was cold it measured about 10psi, so I charged it to 12psi but the problem returned a few days later.
    9. Now that burner is running with a call for heat, it fires back up when the temp drops to about 190 and turns off at about 200.
    10. Circulation sounds are normal with hot water circulating.
    11. It happened again (circulation in baseboard with air sounds, boiler temp down to 60'F without firing, no water pressure on gauge) but boiler fired up when the plumbing system pressurized due to a flushing toilet. So I assumed that the problem was with the low pressure shutoff.
    12. It happened a third time and I tried to trigger the burner to fire by forcing the plumbing system to pressurize but it had effect. That's when I noticed the reset button on the side of the Beckett Burner (see attached picture). I pushed that and everything fired up fine.

    The furnace runs for days without problems before this issue randomly reappears. Questions:
    1. Why did the temp get so low in the boiler? Why so hot? I don't really know when the temperature setpoints are for on the Honeywell strip gauge, I assumed they are for the operating range. Bad temp controller?
    2. Why did the pressure get so low in the boiler? Should it have a pressure of 12psig even when cold? Or just when operating?
    3. What are the proper temperature and pressure operating ranges? (see pic of Honeywell trip switch)
    4. The reset button on the top did nothing but the one on the side got it restarted. What does that indicate?

    I'd take the system apart myself but I can't risk any delay if something goes wrong with this weather we've been having in the Northeast. I hope that your guidance will save me some time and money! I'm leaving for a week long vacation at the end of the month and I am worried about leaving the house alone with a bad furnace.Thank you for your help!
    Attached Images
        
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #2

    Feb 18, 2014, 08:30 PM
    It seems you have a possible combination of problems. The first thing which needs to be addressed is the water situation. You should have 10-12# on the boiler when cold. Some pictures of the near boiler piping would help. You may also have control or motor problems too but the water pressure issue needs to be taken care of first.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

My furnace is set at 70 and the temp drops to 64 before turning back on [ 2 Answers ]

My furnace is set at 70 but the temp. Drops to 64 before it turns back on. Not sure were to start. It has a white-rogers thermostst and it just started doing this

90 accord oil pressure low when warmed up drops to 0 at idle [ 1 Answers ]

I have a 90 accord lx with f22a1 motor with h22 pistons f22 rod and crank using stock f22 headgasket and cars runs but never changed oil pump put in balance shaft eliminator kit on oil pump but didn't change the oil pump was used off the stock 220,000 mile motor. Think it's the oil pump? I put some...

Low PSI and temp on oil burning furnace w/boiler [ 1 Answers ]

I live in a two story very old house. The furnace is an oil burning and uses water to heat. This winter I can get the upstairs to stay near 70 but the downstairs barely gets above 50. I have been told there are two zones but that doesn't help me figure out why one zone heats and one doesn't. I...

Furnace not kicking on when temp drops below thermostat set temp [ 1 Answers ]

I've got a Beckett oil heat water on demand furnace that heats through baseboards. Since this past weekend the furnace hasn't been kicking on when the temperature drops below my set temp of 68 degrees. I have to go down to the furnace and simply touch the top of the reset box for it to kick on. ...

Oil furnace kick in and stop when water temp is high [ 2 Answers ]

Good afternoon, My house is heated with an oil furnace providing heat to a hot water baseboard system. For the last little while, I noticed the burner kicking-in for a few second when the thermostat send the signal (close the circuit) and stop with a second or two. When it does that the water...


View more questions Search