    Pump not pulling water
    Hello I installed a 3/4 deep well above ground pump about 1 1/2 years it was working great then she a problem with the galvanized pipe not holding a prime they pulled the pipe I had water at 50 foot down I put in new pipe to about 60 foot this is a single pipe with a new foot valve in a 2.5 inch well I primed the complete pipe it held the prime with no leaks turned the pump on and it will not pull water up pressurize the system any help with this would be great

    Thank you
    buddyfd912
    jlisenbe's Avatar
    jlisenbe Posts: 5,020, Reputation: 157
    Uber Member
     
    #2

    Feb 9, 2014, 07:59 PM
    50 foot down I put in new pipe to about 60 foot this is a single pipe
    You cannot set up your system in that manner. With a single pipe (shallow well setup), you can only pull from about 25' down. To go to 50 feet, you will need to setup with two pipes and the jet at the bottom with the foot valve.

    I am assuming it was originally two pipes going down.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

We have lost water to our hose, in the pump house the submersible pump motor trips [ 3 Answers ]

We lost water, so we went to the pump house the submersible pump motor tripped, we clicked the reset button and it builds pressure to about 38 PSI then trips again, so we replaced the motor, no change does same problem, so we replaced the 30/50 pressure switch, same problem exists.

I have a problem where my heat pump contactor isn't pulling it. It's a 17 year old W [ 20 Answers ]

I have a problem where my heat pump contactor isn't pulling it. It's a 17 year old Weatherking unit. I saw that I was getting some voltage at the coil so I replaced the contactor. It still didn't pull in, so I checked the voltage again and then I noticed that I was actually getting ~14.5V on...

Does a condenser centrifugal pump suit t work asa chilled water pump [ 0 Answers ]

I have 3 cenreifugal pump which are used for the condenser cooling water recirculation, may I could use it as a chilled water pumps and get another smaller pumps for cooling water recirculation, thank u in advance.

Water heater element pulling juice when should be off [ 3 Answers ]

Last night we seemed to have extra hot water. This morning my wife had very little warm water, which depleted to no warm water, for her shower. I checked the water heater and found it off with a small amount of water present underneath and in casing. I hit the reset and it turned on. This was at...


View more questions Search