    Goodman heat pump auxiliary heat
    Why would a heat pump keep throwing the breaker and switching to auxiliary heat? It is 20 degrees outside, is this normal or is something possibly wrong?
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #2

    Jan 4, 2014, 06:36 PM
    It is not normal & there could be any of several causes. The fact it is tripping the breaker makes me believe there is an overload somewhere. Older Goodman heat pumps were particularly sensitive to having sufficient return air flow. Insuficient return air flow would cause compressor failure.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Auxiliary heat source with goodman heat pump? [ 0 Answers ]

Can we have auxiliary heat source added to existing Goodman heat pump unit?

I have a 4 ton rued heat pump with auxiliary gas heat pump quits working [ 1 Answers ]

I have a 4 ton ruud heat pump with gas pack the heat pump quits when it gets 39F outside and furnice kicks in but does not ignite and I smell no gas what could it be

My Goodman heat pump, model GSH130361AD, in heat mode outside unit does not start up. [ 10 Answers ]

Goodman heat pump, model GSH130361AD, Goodman AEPF series Air Handler, and a Honeywell T8411R t-stat. After wiring and setting everything up, the A/C works very good. In heat mode the aux heat comes on but the outside unit does not start up. Emergency heat works well too. The units are used...

My Trane Auxiliary heat on heat pump is tripping breakers. I think all 3 elements are g [ 0 Answers ]

All 3 white control wires on 3 contactors to elements gets energized at the same time even when only calling for 2-3 degrees increase. Is that normal? I thought it was setup to increase elements based upon the amount of heat called for? The point is breakers keep tripping in winter for the last...

Heat pump auxiliary heat keeps coming on. [ 13 Answers ]

One of our 2 Ruud heat pump keeps cycling on auxiliary heat. The installer says there is nothing wrong, if so why is the other one working properly, plus in the summer it will not get below 76 degrees with that same unit. Freon is fine.


View more questions Search