    Electric forced air furnace won't turn on automatically anymore
    I have a 18 kw 240 v Nortron single phase electric forced air furnace with a digital thermostat, it has worked great for years on auto or if we manually turned the tstat up it would turn on till the temp we set was reached. Now it won't come on with auto or fan on settings only if I hit the continuous air switch on the furnace it will come on until temp is reached then stop heat, could it be a sequencer or relay?
    Thank you in advance for any reply.
    parttime's Avatar
    parttime Posts: 1,440, Reputation: 113
    Ultra Member
     
    #2

    Dec 19, 2013, 03:45 AM
    Hi, could you post a picture of this "continuous air switch" that your hitting?
    ScreamNDemon's Avatar
    ScreamNDemon Posts: 5, Reputation: 1
    New Member
     
    #3

    Dec 19, 2013, 05:44 AM
    I will take pic and upload if necessary but it is just a fan control switch that has two settings; continuous and auto. The furnace has two other switches; 1 is energy saver (mild and cold) on cold, 2 is summer switch (ventillation and heating) on heating. So I'm using the continuous switch to blow the heat because it won't come on on the auto setting.
    Thank you.
    parttime's Avatar
    parttime Posts: 1,440, Reputation: 113
    Ultra Member
     
    #4

    Dec 19, 2013, 06:51 AM
    So what your hitting to get your fan to run is a the limit switch? As below, I'd say change it out. Good luck
    Attached Images
     
    murcam's Avatar
    murcam Posts: 1, Reputation: 1
    New Member
     
    #5

    Nov 15, 2014, 02:51 AM
    Hello, I have a similar problem where the electric fan will run continuously after the thermostat has been turn down. This is a Nortron 21 FA 25. Would the limit switch be the same problem? Look forward to hearing from you

    [email protected]

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Coleman evcon electric blend air II furnace blower won't turn on [ 1 Answers ]

I have a coleman evcon furnace blend air II. The AC will not come on. I replaced the thermostat, furnace blower capacitor and relay. I also replaced the AC dual relay. The AC unit runs when I invoke the contact at the outside unit and the coils cool. But the inside blower still won't cut on. I...

Ruud forced air electric furnace will not start [ 0 Answers ]

I have a Ruud forced air electric furnace. My furnace will not come after call from Thermostat. I hear click from thermostat but the heat does not come on. I tried turning on the air, plus aux heat but they will not come on. I have a Honeywell Programmable Thermostat that sometimes shows a wait...

2 Stage Electric forced air Furnace [ 1 Answers ]

Hello Everyone I am currently having a problem with my 2 stage electric forced air furnace. I have searched everywhere for information but to no avail. The furnace is probably a 1975 model... this is the information I have... Lear Siegler (Home Division) Model MEF65 Last winter while I was...

I have a Ruud forced air electric furnace. My furnace will not shut off. [ 1 Answers ]

The fan and heat run continuously. I even disconnected the thermostat wires and it still won't shut off until I throw the breaker.

Forced Air Gas Furnace Fan Won't turn off [ 1 Answers ]

We have a Forced air gas furnace with a programmable thermostat. What is happening is that the furnace will turn on when the temp drops, like it is supposed to, and the fan will come on to blow the hot air, but the fan doesn't turn off. It will continue to blow even when the air is cold coming out...


View more questions Search