    Goodman furnace ignitor will not glow.
    I have a goodman furnace, 1994 model. When you turn it on you get a constant light (normal condition) but the ignitor will not glow. After a short period I get a continuous flash. The code table says there is a "twinning" issue and to check the polarity. Don't know what this means or what to check.
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #2

    Dec 16, 2013, 04:28 PM
    To check the polarity, you need a voltmeter capable of reading 150 volts AC. Check the black in coming wire to ground. You should get +/- 120 volts AC. Then check the incoming white to ground. You should get virtually nothing. If you get voltage on white but not on black, reverse them.
    My guess is the polarity is OK but you have a bad board. The twinning thing only comes into play if you have two furnaces tied together.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman furnace HSI does not glow, burners never light [ 3 Answers ]

I have a Goodman gas-forced air furnace, about 10 years old. I have power to the main control panel (part# 18099-13) and gas is "on". In the furnace sequence posted by sticky, I am having problems at the step where the hot surface ignitor "glows" to light the burners. All other steps, such as the...

Furnace ignitor doesn't glow [ 0 Answers ]

When the stat calls for heat the blower runs for a while then shuts down, then the inducer runs for a while then shuts down, at no time does the ignitor glow. I put a meter on the wires going to the ignitor and found no power during the start up sequence. Also error code 32 flashes.

6yr old goodman furnace won't run.. had ignitor replaced in 04, could it be out again [ 1 Answers ]

6yr old goodman gmt090 running this morning at 830, left house came back 230, house cold reading 57 degrees. Had ignitor replaced in feb of 04, could it be out again..

Goodman furnace ignitor problems [ 7 Answers ]

Having an issuse with my goodman furnace. Ignitor turns red, flame comes on, and then goes out. Ignitor will head up again, flame on, and then off. THis repeats. I've taking off the sensor and cleaned it to a sparkly new look. Taken the burner housing out and cleaned them individually of all...

No Ignitor Glow [ 8 Answers ]

Not sure the brand.. When I have the thermostat call for heat the vent blower and the blower both come on and there is no glow.. I have tested and bypassed the limit switches and that doesn't fix the problem. Now the diagnoses light flashes 4 times which is supposed to mean that there is an open...