    Bryant furnace turns flame off before set temperature is reached.
    I have a Bryant Induced-Combustion Gas Furnace, model 373LAV Downflow & 383HAV Upflow. Mounted horizontally. It turns off flame before set temperature is reached, and recycles immediately.

    Sequence is:

    Inducer starts
    After 25 sec. the ignitor glows
    After 8 sec. the flame lights
    After 45 sec. the blower fan starts
    After 2 min. 21 sec. the flame goes out
    Indicator light flashes 33
    After 5 sec. the inducer fan stops
    After 3 min. 58 sec. the blower motor stops
    Inducer starts immediately
    And it's the same cycle over again.

    Clean filter, and no intake restrictions.
    Doesn't appear to be cracked heat exchanger (no blowback)
    Flames are blue and appear to be confined to the exchanger ports (no roll-out)
    Thermostat anticipator has not affect
    RobertShaw mercury switch thermostat level

    I cannot inspect the vents close-up, they are in high ceiling. But, I cannot detect much air from the vents.

    It is 20 degrees F outside. The thermostat is set to 72, but the temperature does not get above 64.

    What do you think?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Nov 25, 2013, 07:26 PM
    You show a model for upflow and downflow but have it mounted horizontally? Is it rated for horizontal applications? Some are and some aren't. Heat exchangers may be laid out differently. Could be overheating and the thermal overload is shutting down the gas. From your description of operation, it sounds like it is operating properly. I also noted your "low airflow" comment. If you have a collapsed or restricted duct, that will also trip the thermal overload due to an overheated plenum.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heat running in aux mode but has reached the set temperature? [ 0 Answers ]

This morning my centeral heat and air unit made a squealing racket. Now, the thermostat is set at 70 and the temp says 70 but the auxiliary mode is running and I don't have it set to run... What can be wrong

Thermostat doesn't shut off after set temperature is reached [ 0 Answers ]

We have an electric unit with a heatpump (2 systems, 2 different thermostats)> It is 27 degrees outside, and the heat won't shut off. I have the thermostats set on 72 and 70 degrees, and both show that as the inside temperature. It runs and runs and runs, and if you kick it up 1 degree, the aux...

AC unit turns off before set temperature reached [ 1 Answers ]

I have a 13 SEER RUUD heat pump 4 ton size in my Florida house. It it 4 years old with a programmable Hunter 43154 thermostat. The unit is coming on periodically and blowing cool air, but it turns off before the set temperature is reached. The thermostat says the room is 88 degrees. We have it set...

Gas furnace turns off before set temperature. [ 3 Answers ]

We have Janitrol / Goodman GMP Series gas furnace. Recently, the furnace would turn off before set temperature on the thermostat. I had a Lux programmable thermostat and thought this was the problem. I replaced the thermostat with a Honeywell programmable thermostat and it worked great. The...


View more questions Search