Pressure switch open with inducer on?
I have a concord 80 plus furnace. I tried turning it on and it runs for a few seconds and shuts off. Sometimes it will ignite and sometimes it won't. I replaced the flame sensor and the pressure switch, I have sucked/blown on the tube and cleaned what the tube connects to with a small piece of wire but no luck. I also go on the roof and checked the flue or whatever the pipe is up there and it is not clogged that I can see. The LED light on the circuit board is flashing three times which should mean the pressure switch is open with the inducer on.
|
|
 |
Ultra Member
|
|
Oct 27, 2013, 09:03 AM
|
|
You will need a volt meter to confirm the switch is actually open. Do you have one & know how to use it?
|
|
 |
New Member
|
|
Nov 10, 2013, 11:38 AM
|
|
 Originally Posted by Grady White
You will need a volt meter to confirm the switch is actually open. Do you have one & know how to use it?
I am having the same problem and stumbled across this page. I have a volt meter and know how to use it, I just don't know how to check the switch.
|
|
 |
Ultra Member
|
|
Nov 10, 2013, 02:46 PM
|
|
Teknik:
Set the meter for AC volts. Have the furnace calling for heat & the venter running. Measure voltage across the switch. If you get +/- 24 volts, the switch is indeed open. No voltage indicates a closed switch.
Exactly what is the furnace doing? Try to be as detailed as possible.
|
|
 |
New Member
|
|
Nov 10, 2013, 08:13 PM
|
|
Hey thanks for the reply. I'm not freezing or anything because the furnace is running right now.
It's weird. It will work for a month, then stop. I'll go restart it and it will do 1 of 3 things.
1. Fan comes on, no flames appear in the box, shuts off and gives the inducer on error
2. Fan comes on, Flames shoot for about a second, shuts off and gives the same message.
3. Furnace starts normally, runs 10 minutes, then shuts off.
I know it's not the air intake. That was easy to check.
I know it's not the exhaust. I popped the pipe off and just let it try to run it a couple times with no luck.
I've sucked on more hoses than I can count.
I took out the thermostat out of the box and cleaned it.
None of the water hoses are clogged
I ran the water pump a couple times by pouring water into it.
I'm not sure what else it could be. It may just be that switch and sometimes it works, sometimes it doesn't.
|
|
 |
Ultra Member
|
|
Nov 11, 2013, 08:22 PM
|
|
Grrrr. I hate intermittent problems. I'm crazy enough without having to deal with a furnace which will work just fine while I'm there but such is the life of a service guy.
It is possible there is some junk intermittently blocking the port(s) to which the pressre switch connects. I've often used a small drill bit to clean them. If it's a piece of rust or something like that, sometimes you'll just push it out of the way for the time being.
|
|
 |
New Member
|
|
Nov 12, 2013, 10:43 AM
|
|
 Originally Posted by Grady White
Grrrr. I hate intermittent problems. I'm crazy enough without having to deal with a furnace which will work just fine while I'm there but such is the life of a service guy.
It is possible there is some junk intermittently blocking the port(s) to which the pressre switch connects. I've often used a small drill bit to clean them. If it's a piece of rust or something like that, sometimes you'll just push it out of the way for the time being.
I may just replace the switch if I can figure it out, and I can't imagine it's that hard. The furnace is a Duquesne ,an it's only 3 years old. We've been having this problem since it's second year as far as I can remember.
|
|
 |
Ultra Member
|
|
Nov 12, 2013, 07:44 PM
|
|
99+% probablility the pressure switch is not the problem.
|
|
 |
New Member
|
|
Mar 26, 2014, 02:51 PM
|
|
For anyone that comes across this post looking for an answer like I did...
Shortly after my post on Nov 12, 2013 I got the same problem again. I went down and firmly tapped on the pressure switch with a nut driver (just needed something blunt to hit it with) and it's worked fine since. I'd imagine it's a temp fix to a permanent problem, but I think I know it is the switch now.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
"pressure switch open with inducer on?
[ 53 Answers ]
I have an intertherm propane furnace, new in 2006 we just turned propane back on for the year, and it won't light. The red light is blinking 2 times & indicates "pressure switch open with inducer on" however I have no idea what that means or how to troubleshoot to fix. It hums like always before it...
Open pressure switch with inducer motor running
[ 0 Answers ]
I have 3 flashes when the furnace shuts off inducer is still running.When it shuts down wait a few min and the furn. Comes back on again.Is this normal operation?I do have a drain opposite side of the inducer.Is that on the wrong side of the furnace.Concord 95.
Pressure switch open with inducer on
[ 5 Answers ]
Hello all. I have a Gibson forced air furnace I've been having trouble with the last couple of days. At first, the unit would start up... Inducer comes on, about 20 sec later the ignition coil starts to glow, the gas would turn on and ignite and it would run for a short period. There is an amber...
View more questions
Search
|