  • Oct 26, 2013, 02:18 PM
    lacey8434
    Pressure switch open with inducer on?
    I have a concord 80 plus furnace. I tried turning it on and it runs for a few seconds and shuts off. Sometimes it will ignite and sometimes it won't. I replaced the flame sensor and the pressure switch, I have sucked/blown on the tube and cleaned what the tube connects to with a small piece of wire but no luck. I also go on the roof and checked the flue or whatever the pipe is up there and it is not clogged that I can see. The LED light on the circuit board is flashing three times which should mean the pressure switch is open with the inducer on.
  • Oct 27, 2013, 09:03 AM
    Grady White
    You will need a volt meter to confirm the switch is actually open. Do you have one & know how to use it?
  • Nov 10, 2013, 11:38 AM
    Teknik
    Quote:

    Originally Posted by Grady White View Post
    You will need a volt meter to confirm the switch is actually open. Do you have one & know how to use it?

    I am having the same problem and stumbled across this page. I have a volt meter and know how to use it, I just don't know how to check the switch.
  • Nov 10, 2013, 02:46 PM
    Grady White
    Teknik:
    Set the meter for AC volts. Have the furnace calling for heat & the venter running. Measure voltage across the switch. If you get +/- 24 volts, the switch is indeed open. No voltage indicates a closed switch.

    Exactly what is the furnace doing? Try to be as detailed as possible.
  • Nov 10, 2013, 08:13 PM
    Teknik
    Hey thanks for the reply. I'm not freezing or anything because the furnace is running right now.

    It's weird. It will work for a month, then stop. I'll go restart it and it will do 1 of 3 things.
    1. Fan comes on, no flames appear in the box, shuts off and gives the inducer on error
    2. Fan comes on, Flames shoot for about a second, shuts off and gives the same message.
    3. Furnace starts normally, runs 10 minutes, then shuts off.


    I know it's not the air intake. That was easy to check.
    I know it's not the exhaust. I popped the pipe off and just let it try to run it a couple times with no luck.
    I've sucked on more hoses than I can count.
    I took out the thermostat out of the box and cleaned it.
    None of the water hoses are clogged
    I ran the water pump a couple times by pouring water into it.

    I'm not sure what else it could be. It may just be that switch and sometimes it works, sometimes it doesn't.
  • Nov 11, 2013, 08:22 PM
    Grady White
    Grrrr. I hate intermittent problems. I'm crazy enough without having to deal with a furnace which will work just fine while I'm there but such is the life of a service guy.

    It is possible there is some junk intermittently blocking the port(s) to which the pressre switch connects. I've often used a small drill bit to clean them. If it's a piece of rust or something like that, sometimes you'll just push it out of the way for the time being.
  • Nov 12, 2013, 10:43 AM
    Teknik
    Quote:

    Originally Posted by Grady White View Post
    Grrrr. I hate intermittent problems. I'm crazy enough without having to deal with a furnace which will work just fine while I'm there but such is the life of a service guy.

    It is possible there is some junk intermittently blocking the port(s) to which the pressre switch connects. I've often used a small drill bit to clean them. If it's a piece of rust or something like that, sometimes you'll just push it out of the way for the time being.

    I may just replace the switch if I can figure it out, and I can't imagine it's that hard. The furnace is a Duquesne ,an it's only 3 years old. We've been having this problem since it's second year as far as I can remember.
  • Nov 12, 2013, 07:44 PM
    Grady White
    99+% probablility the pressure switch is not the problem.
  • Mar 26, 2014, 02:51 PM
    Teknik
    For anyone that comes across this post looking for an answer like I did...

    Shortly after my post on Nov 12, 2013 I got the same problem again. I went down and firmly tapped on the pressure switch with a nut driver (just needed something blunt to hit it with) and it's worked fine since. I'd imagine it's a temp fix to a permanent problem, but I think I know it is the switch now.