    Aluminum Feeder Terminations
    As a commercial electrician I was taught that terminations of Aluminum feeders had to be periodically checked for tightness due to 'creep' (the wire expanding and contracting due to changes in temperature). Is this a real problem? What is the recommended interval for checking the proper torque of the terminations?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Mar 29, 2007, 02:47 PM
    All electrical equipment, including copper cable mechanical connections, bus bar bolted connections, circuit breaker bolted connections, etc. are recommended to be inspected and checked for proper torque values, periodically, usually annually.

    This recommendation is from NEMA, IEEE, ANSI, and every manufacturer of electrical distribution equipment.n

    Loose connections wire is not unique to aluminum. What is unique to aluminum is the soft characteristic of the metal, which gives the wire the false impression that it needs to be tightened frequently.

    If you tighten a connection today, you surely can get a few more turns on the bolt or screw a few days later. All you are doing is crushing the wire, causing the metal to be pressed into any voids that may be in the mechanical connector.

    This softness is not as noticeable with copper, so the impression is that copper is less apt to loosen while aluminum is more apt to loosen. If connections are torqued to the value listed on the mechanical connector, no more tightening is necessary.

    High current loads create heat, which causes any metal to expand, and ultimately there is cooling, so the temperature changes of connections , along with vibration of equipment and just the nature of these metals cause any connection to loosen over time.

    I manage a crew of electricians/technicians that perform these annual inspections using some high tech equipment, such as infrared cameras, ultrasound detectors, DLRO, (Digital low resistance ohmmeter), and millivolt DVM, to locate and quantify loose connections while equipment is both energized and de-energized. We have done this in paper mills, hospitals, data centers, foundries, office buildings, shopping plazas, etc, etc.

    We even have one customer that hires a helicopter for us to inspect their couple hundred miles of power lines Which those by the way are all aluminum wire, and we find few problems.

    While aluminum cable and bus is very popular, you may be surprised that most loose connections are found with copper wire and bus, and the typical brass,copper and copper alloy mechanical connectors. And you may be surprised that tightening a connection too much can be worse than a loose connection, review this page: The Loose Electrical Connection Myth

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

400 Amp , Feeder Wires? [ 3 Answers ]

We Have A 400 Amp Service, What Size Should The Feeder (wires) Be? Need To Know Thanks Please Help Arvind

Feeder size [ 1 Answers ]

Hi, We are building a small art studio in our backyard. The power requirements for the building are: 1 dedicated 110V 20 amp circuit for a small kiln 1 dedicated 220V 20 amp circuit for a larger kiln 1 dedicated 110V 15 amp circuit for small wall-mounted heater/ac unit 1 dedicated 110V 15...

PEX and Stubouts / Terminations [ 2 Answers ]

I decided to use PEX in my renovation with a manifold/home run set up. Have already pulled all the tubing to each fixture, the manifolds have been mounted and connected, no leaks all is well. I'm undecided on how to handle the termination of each fixture tube. Under cabinets (kitchen island sink,...

Feeder Wire for Sub-Panel [ 2 Answers ]

Hello my name is Mark and I have just purchased my first home. I was hoping someone could help me out in determining what size feeder cable I would need to run from my main panel to a detached garage. The length of the run would be 70 feet. The main panel is a 100 amp panel. I would be running 6...

Feeder line from main panel [ 5 Answers ]

I want to run a feeder line from one building to another in a 2 in. underground conduit.about 100 ft. run what size alum. Wire will I need for 125 amp sub panel


View more questions Search