    Furnace will not start
    I tried my furnace for the first time since winter and it would not ignite, the blower works but the element that use to glow to start the flames will not glow. It's a Goodman model number GMP075-3 REV A, serial number 9709824941. Which should I change out?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Sep 17, 2013, 07:05 PM
    I would start with the ignitor. Test continuity with an ohmmeter, it should be 0 or close to it. If it reads infinity or very high resistance you should replace it. On most Goodman /Amana, it is a pretty easy job and the parts are less than $50.
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #3

    Sep 17, 2013, 07:07 PM
    Which blower are you talking about? Is it the small exhaust blower or the fan which circulates air around the house?
    vickersb2's Avatar
    vickersb2 Posts: 4, Reputation: 1
    New Member
     
    #4

    Sep 18, 2013, 03:20 AM
    Quote Originally Posted by Grady White View Post
    Which blower are you talking about? Is it the small exhaust blower or the fan which circulates air around the house?
    Blower that circulates the air around the house.I remember the igniter use to glow and then the flames would start. I had problems with the flame sensor last year but I pulled it out and sanded it lightly and then the flames would stay lite.
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #5

    Sep 18, 2013, 05:00 PM
    Before the ignitor glows, the exhaust blower should start. Use a voltmeter to make sure you are getting 120 volts to the venter motor. If you are & the motor does not start, shut off the power & use a small screwdriver to try to turn the motor. If it turns, turn it 2 or 3 revolutions then try the furnace again. Sometimes the motor gets stuck over the summer.
    vickersb2's Avatar
    vickersb2 Posts: 4, Reputation: 1
    New Member
     
    #6

    Sep 20, 2013, 04:45 PM
    I put in new igniter and no luck. The error code light blinks quick 3X. The exhaust blower is working fine. HHMMMMM
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #7

    Sep 20, 2013, 04:58 PM
    I wouldn't mess around much more... can get costly replacing parts that don't need to be replaced... ;)

    Contact Goodman furnaces directly and talk to the technical service department:

    GoodmanŽ Manufacturing - Air Conditioning and Heating for Commercial and Residential Products

    Have an electrical tester handy when you call!

    Mark
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #8

    Sep 20, 2013, 05:04 PM
    Three blinks indicates a pressure switch failing to close. Check the vent pipe & chimney for any obstructions.
    vickersb2's Avatar
    vickersb2 Posts: 4, Reputation: 1
    New Member
     
    #9

    Sep 27, 2013, 05:35 AM
    Quote Originally Posted by Grady White View Post
    Three blinks indicates a pressure switch failing to close. Check the vent pipe & chimney for any obstructions.
    That is what it was , vent nipple on top of the fan was rusted shut so no air could go through. I pushed a piece of copper wire through and works now. I have to buy a new gasket now, the old one fell apart when I took the fan off. Thanks for all the help guys.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bryant furnace showing code 12-blower on after power up. Furnace won't start. Why? [ 0 Answers ]

Blower motor on all the time. No heat from furnace. Why?

Gas furnace blower motor won't start/slow to start [ 0 Answers ]

I have a airtemp probably 70's model we had to replace the blower motor about two years ago. Now when the fan is supposed to start it either won't start or is very slow to start. When this happens you can manually move the squirrel cage and it runs great through the complete cycle. We just replaced...

Furnace start up [ 1 Answers ]

I have a bryant furnace model #394gaz036100aafa and when call for heat it click click Comes on for a few seconds and shut down.I think it maybe the flame sensor is dirty Or needs to be replace.or something else .thank you for any response ...

Furnace ignites but blower won't start till furnace shuts down. [ 7 Answers ]

(Nordyne/Miller G3RA)-I have a furnace HSI(glow plug) that will ignite and burn until it gets too hot and shuts down. As soon as the furnace shuts down the blower starts to circulate air. The blower circulating air cools the furnace and it reignites.Shortly after the furnace ignites the blower...

Gas furnace has an intermittent pilot, pilot lights, furnace tries to start [ 3 Answers ]

Have a 25 plus year old furnace pilot will start when signal sent furnace tries to start makes noise as it tries over and over but will not start. Thanks


View more questions Search