    DIYCECEKAT's Avatar
    DIYCECEKAT Posts: 3, Reputation: 1
    New Member
     
    #1

    Sep 5, 2013, 07:04 PM
    Installed new fan motor and capicator but AC unit won't start
    My AC began squealing one night so I cut it off and called the HVAC contractor that installed the unit and that services the unit each year (had just serviced it 30 days prior) When they turned the unit on it did not squeal but ran fine, the tech said it could the motor going out and to check, the next time it made the noise, to see if the fan was moving. The unit ran consistently for 4 days and then the squeal started and the fan was not running. I cut if off and waited and started it again the next day I woke up and it would not turn on. I replaced the motor and capacitor (the unit had a 60/5 440 capacitor, but when I ordered the motor they said it should take a 45/5 370 capacitor which they sent me. After installing the motor I decided to leave the old capacitor (wasn't sure if the new one was right) then turned on the breakers and the thermostate and noting... the inside blower comes on but the outside compressor and fan did nothing. The contactor clicks in, but nothing starts. So I don't know what to do... My unit does not have a fuse or separate breaker because it is next to the electrical panel. Is there a reset button or something else that I should try. Any help would appreciated.
    dewey066's Avatar
    dewey066 Posts: 49, Reputation: 1
    Junior Member
     
    #2

    Sep 6, 2013, 02:56 AM
    The job of the capacitor is to give it a "kick" to get it moving. On the side of the motor itself it will say the correct capacitor for the motor. I'm sure they sent you the correct one with the new motor.

    The motor probably won't work without a good capacitor, it will try and run and overheat the start windings inside the motor (the start winding are very thin strands of copper wire, and can be burnt-out very quickly if it is drawing excessive amperage, which happens with a bad/dead capacitor). The motors have an internal thermal switch which opens once hot (from trying and failing to start) and automatically closes once it cools down.

    The voltage rating (330V vs. 440V) is not that important and are interchangeable for the most part. The capacitance rating is the important thing and can be tested with a good multi-meter (always shut power off to the unit before attempting anything!! ).
    This value must be within 10% of the rating, so a 5MFD, or uF rating would have to read at least 4.5, and not more than 5.5. The small number is the Fan Capacitance and the large number is the compressor motor capacitance.

    Try replacing the cap. With the once they sent you and make sure that you are getting 230V across both wires, on both sides of the contactor. A bad circuit breaker can give you two 110V legs to ground, but Zero or 440V across the two wires, in which case you would need to replace the breaker. Also check the contactor itself, when it is calling for cooling (the relay coil on the contactor should be "pulled-in" and making a connection. There should be no voltage drop across the contactor (a meter reading volts would read Zero going across the relay when "on").

    Does the compressor attempt to run (either runs or give a quick hum and then stops? Again there is a thermal switch here as well. A quick hum is good and expected if you are still using the bad capacitor.
    DIYCECEKAT's Avatar
    DIYCECEKAT Posts: 3, Reputation: 1
    New Member
     
    #3

    Sep 6, 2013, 10:49 AM
    Thank you for your response. I did install the new cap that they sent with the motor and still nothing. There are no sounds coming from the unit at all. There is power going to it. At first the contactor would suck in when the power was turned on.. no it is in but there is nothing going on. Is there a way to reset the unit? I'm going to try and measure the voltage on the contactor.. Thanks again.. This value must be within 10% of the rating, so a 5MFD, or uF rating would have to read at least 4.5, and not more than 5.5. The small number is the Fan Capacitance and the large number is the compressor motor capacitance.

    Try replacing the cap. With the once they sent you and make sure that you are getting 230V across both wires, on both sides of the contactor. A bad circuit breaker can give you two 110V legs to ground, but Zero or 440V across the two wires, in which case you would need to replace the breaker. Also check the contactor itself, when it is calling for cooling (the relay coil on the contactor should be "pulled-in" and making a connection. There should be no voltage drop across the contactor (a meter reading volts would read Zero going across the relay when "on").

    Does the compressor attempt to run (either runs or give a quick hum and then stops? Again there is a thermal switch here as well. A quick hum is good and expected if you are still using the bad capacitor.[/QUOTE]
    DIYCECEKAT's Avatar
    DIYCECEKAT Posts: 3, Reputation: 1
    New Member
     
    #4

    Sep 6, 2013, 05:20 PM
    The contactor was the culprit this time... installed new one and now AC is working

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Installed new motor and fan in heat pump, it will not start [ 1 Answers ]

Replaced fan and motor and start capacitor in Pool heat pump. It will not start. Large capacitor is leaking a small amount of sticky black fluid at top, it is placed upside down in holder.?

Loud Humming Noise after new blower fan and motor installed in Lennox unit [ 1 Answers ]

I have a G50UH Lennox and the blower fan got wobbly and started thumping and screeching at the end of cycles, so I had a new blower fan, squirrel cage and fan motor installed on Monday. I told the tech it sounded very loud to me and he shrugged and said at least it's not thumping and bumping like...

I put a new capicator in my ac and I still have to use a stick to start the fan [ 1 Answers ]

I have a 1994 comfort maker central air conditioner and the fan on the motor won't spin on its own. I put a new capicator in also, do I need a new motor how much is this?

RHEEM A/C Unit blower motor won't start [ 5 Answers ]

I have a problem with my RHEEM air package unit Air and heating, the blower motor won't start and it keeps blowing my 24v transformer, transformer literally blows up by doing an explotion noise. Now I am thinking that it might be the blower motor it self the one returnig High Voltage power to my...

Fan motor and capicator [ 1 Answers ]

Can anyone tell me where I may purchase parts for a Rheem Classic Airconditioning unit? I am in need of a Fan motor and a capicator. Thank you


View more questions Search