    Heat pump
    Hello again
    I have a question
    I have a ducane 2 tons heat pump it work fine on cooling but when is switched to heat high discharge pressure goes to over 300 psig and suction pressure goes down to 0 psig and outdoor unit shut off, filter is clean, blower is fine unit runs for about 1 minute
    Thank for any help I can get on this
    NorthernHeat's Avatar
    NorthernHeat Posts: 1,455, Reputation: 132
    Ultra Member
     
    #2

    Mar 22, 2007, 02:05 PM
    Sounds like a restriction in the outside piston (metering device) If the head pressure went to 300 and the suction stayed aroung 50 or so I would say it is poor indoor airflow.
    Clough's Avatar
    Clough Posts: 26,677, Reputation: 1649
    Uber Member
     
    #3

    Mar 22, 2007, 02:06 PM
    You might want to check out what you find by using the following link:

    www.ducanehvac.com/res/pdfs/ac/20407501.pdf

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

NO HEAT! Janitrol heat pump and AC system. Changing to Lux Thermostat. Wiring issue. [ 11 Answers ]

I have a Janitrol A/C and heat pump system. I replaced the thermostat with a Lux T9000LC The A/C works fine, but the heater does not. I have it wired as follows: G - Green Y - Yellow W - White RH - Pink B -

Electric Heat-Pump-No heat [ 2 Answers ]

I had a wall-mounted unit installed in a room in may of this summer. In the middle of the night the heat shut off and has not come back on since. It is an Amana, electric heat with heat pump unit. The cooling works, the heating setting does not blow air at all. When I remove the cover it says...

Heat pump stuck in heat mode [ 4 Answers ]

I have a heat pump that seems to be stuck in heat mode. When you try to turn the a/c on it runs heat. I got the a/c to run by cycling the power a couple of times but after having to use the heat again, it is stuck again. Could this be an electrical problem or is it probably the reversing valve?

Electric heat pump auxilery heat problem [ 4 Answers ]

Equipment: Trane XL1400 4 years old Auxilery heat: Strips... 2 -60Amp circuits Filters changed every 30 days I cleaned outdoor unit summer 2006, as every year. Thermostat: Honeywell Chromotherm II Problem: I have been noticing at times the aux heat kicking in at times I think it should not....

Heat pump vs electric heat [ 3 Answers ]

I have a heat pump with a two stage thermostat, 1st stage is heat pump, 2nd stage is electric (resistance) heat. Is it ever more economical to run the furnace with resistance heat only, not the heat pump? I know that the outdoor temperature affects the ability of the heat pump to work, but is...


View more questions Search