  • Mar 22, 2007, 01:53 PM
    moncagua
    Heat pump
    Hello again
    I have a question
    I have a ducane 2 tons heat pump it work fine on cooling but when is switched to heat high discharge pressure goes to over 300 psig and suction pressure goes down to 0 psig and outdoor unit shut off, filter is clean, blower is fine unit runs for about 1 minute
    Thank for any help I can get on this
  • Mar 22, 2007, 02:05 PM
    NorthernHeat
    Sounds like a restriction in the outside piston (metering device) If the head pressure went to 300 and the suction stayed aroung 50 or so I would say it is poor indoor airflow.