    Hvac
    My blower run continue even I trun off the system at the thermalstate.
    My blower use a relsy not contral broarf.
    My blower have three wire white black and red. So the what (w) conect to com from the transformer and main power. Redconect to the relsy.
    I replace the relay but not help.
    What should I for to fix it?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    May 3, 2013, 06:31 AM
    The relay should close when 24 volts is present, and the contacts should open when 24 volts is removed. A short in the control wiring may keep relay energized. Verify contacts open when voltage is removed from relays coil.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Hvac [ 3 Answers ]

Why my blower doesn't stop

Hvac help [ 0 Answers ]

My unit stopped working. Even the digital thermostat died. I put backup batteries in, reset at the fuse box, and got about 30 minutes working air. I removed the batteries to see if the electricity to the thermostat was still working and a few minutes later the unit stopped working again as did the...

Hvac [ 0 Answers ]

I have a 1000 sq. foot restaurant/hookah smoking lounge. Some of my customers are complaining about the indoor smoke. Since I don't want to make my restaurant a non - smoking restaurant, what do you suggest as far as the best type of ventilation for this type of an application. Will you please be...

Hvac [ 1 Answers ]

Heat pump blowing cold air


View more questions Search