  • May 3, 2013, 06:20 AM
    chang76
    Hvac
    My blower run continue even I trun off the system at the thermalstate.
    My blower use a relsy not contral broarf.
    My blower have three wire white black and red. So the what (w) conect to com from the transformer and main power. Redconect to the relsy.
    I replace the relay but not help.
    What should I for to fix it?
  • May 3, 2013, 06:31 AM
    Stratmando
    The relay should close when 24 volts is present, and the contacts should open when 24 volts is removed. A short in the control wiring may keep relay energized. Verify contacts open when voltage is removed from relays coil.