    wiring water wells 220V - 40A - 400ft
    How could I extend wiring from the subpanel to the water well 400ft away? The subpanel is connecting to the main panel using the #2 wire and 100ft from the main panel. I am thinking about 2 options:
    1) With subpanel: Using load panel or what subpanel to use for each 200ft section? Running 2x200ft which wire size #6, #4, or #2?
    2) Without subpanel: Running 400ft which wire size #4 or #2 directly from the subpanel to the water well?

    What is the best way and why to supply power to the water well 400ft away?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Mar 31, 2013, 07:13 AM
    You keep referring to things as "the well" and "the panel" like we know what you are talking about already.

    You need to begin by giving us some detail about this project.
    How big is the well pump?

    I also have no idea what you are asking in #1).
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #3

    Mar 31, 2013, 07:35 AM
    400 ft is the same whether you run a single 400 or 2 X 200. What purpose is a subpanel? Before you can choose the wire you need the load rating for the pump. BTW 400 ft is a long way from the house for a well, considering the cost of piping and labor install, friction loss etc.
    dukedo's Avatar
    dukedo Posts: 3, Reputation: 1
    New Member
     
    #4

    Mar 31, 2013, 08:22 PM
    I like to run power from the house to the water well about 500ft away from the main panel with the current subpanel already in place.
    I already run 100ft from the main panel rating 200A to the subpanel using #2 wire for the shed. Now, I need to run another 400ft to the water well. I could use another subpanel in between the 400ft or just another junction box to make the run easier due to the length. What size of the wire should I use?

    The load should be around 220Vx30A = 6600W for the well pump.


    Hopefully, that is clear up a little bit. Thank you all for your quick response.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #5

    Mar 31, 2013, 09:07 PM
    Quote Originally Posted by dukedo View Post
    I like to run power from the house to the water well about 500ft away from the main panel with the current subpanel already in place.
    I already run 100ft from the main panel rating 200A to the subpanel using #2 wire for the shed. Now, I need to run another 400ft to the water well. I could use another subpanel in between the 400ft or just another junction box to make the run easier due to the length. What size of the wire should I use?

    The load should be around 220Vx30A = 6600W for the well pump.


    Hopefully, that is clear up a little bit. Thank you all for your quick response.
    @
    Southwire voltage drop calculator indicates #2 copper. I used 240VAC and 30 amps
    dukedo's Avatar
    dukedo Posts: 3, Reputation: 1
    New Member
     
    #6

    Mar 31, 2013, 09:39 PM
    Thank you ma0641.

    It will be costly about $3,000 but to get a new service at the pump in will cost about $7,000. I am thinking about a remote solar pump system too but I don't know much about it and may cost more than $5,000. I think this the best way.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #7

    Apr 1, 2013, 04:02 AM
    No joke here. Wouldn't it be easier, cheaper and more logical to put in a new well closer to the house?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #8

    Apr 1, 2013, 09:59 AM
    Don't think a solar outfit would supply enough power. Even with that you would need a lot of batteries and if you use the well a lot, on a cloudy day, may deplete the batteries. Really, I had a 300 ft. drilled well installed with pump, piping to house(100 ft) and tank for less than $5000

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Submerged water wells [ 1 Answers ]

Water runs from union opened at top of casing at fairly good rate for a short period and will suddenly fall off to practically nothing. Pump still runs but seems that it may be running the water column dry faster than the ground water can refill the space. Considering blowing base out with air..?...

Wells - Causes of Low Water Pressure [ 2 Answers ]

I have low water pressure in my house, which is supplied by a well system. It seemed to have happened over a months time, but is now to a point where it is difficult to take a shower. The pressure gauge was bad, so I replaced it, and the on/off presures seem to be good. The pump goes on around...

Water pressure, wells [ 3 Answers ]

We have a 120' deep well. The bladder tank is good. Just replaced the pressure switch. The house water is okay but when I turn on the outside water hose, all water drains from the bladder tank and the water runs out. The pressure switch runs the pump constantly till it gets hot and shuts...

Need to run 400ft of 110v [ 3 Answers ]

I'm thinking of putting a 1/2 hp fountain in the lake behing my home. It needs 750 watts. The fountain comes with a 100ft gfci cord with standand plug. Since this is a portable fountain, I was figuring on just running 300ft of decent extension cords (12 gauge home depot). However my friend said I'd...


View more questions Search