How to install a wye in PVC under a slab
After the concrete has been removed from above the pipe and the PVC cut to accommodate the length of the wye how do I install the fitting ? Is there some type of slip fitting that is trustworthy?
|
|
 |
Uber Member
|
|
Mar 12, 2013, 06:28 PM
|
|
You can use a repair "slip" fitting. It doesn't have a stop in the middle. Basically you cut the pipe, install the repair fitting WITHOUT glue and slide it up the pipe. Measure the pipe so you know where the middle of the slip fitting is located. Then you install the Y, a small stub out and slide the repair fitting down, working quickly with a lot of glue. If the Y is above grade, use a shielded rubber "Fernco" fitting.
|
|
 |
Senior Plumbing Expert
|
|
Mar 13, 2013, 09:19 AM
|
|
I got to tell you that slip couplings are usually more trouble that they are worth in underground aplications... just too large to work with! Maybe you could use one, but not two and properly PRIME the couplings and pipe, too!
Instead, in my opinion, you would be better off purchasing two shielded band clamps and installing them by sliding the clamps over the cut pipe ends, folding the rubber sleeves back on themselves and installing the wye fitting with 4" pieces of pipe in the both ends of the wye fitting. Flip the rubbers back over, slide the clamps in place and tighten all up.
Be sure to deduct a 1/2" ((2) x 1/4" of rib in between each rubber sleeves) from the overall measure of the pipe piece you cut out from the main drain line...essential for this to work!
See images below
Mark
PS: Ignore the 12" as this was just a number I threw up... your wye fitting and two 4" pieces of pipe will be longer!
|
|
 |
Uber Member
|
|
Mar 13, 2013, 11:38 AM
|
|
Even though I have used slip type fitting for small pipe repair, my choice would be as Mark has shown but not under concrete.
|
|
 |
Eternal Plumber
|
|
Mar 13, 2013, 11:54 AM
|
|
That's the way I do it Mark but instead of using a regular wye I would use a street wye (see image) Same difference but less work. And I would use shielded couplings above or below ground,Regards, Tom
|
|
 |
Senior Plumbing Expert
|
|
Mar 13, 2013, 11:56 AM
|
|
Why not under Concrete, Brian? This is an accepted standard practice for a couple decades now... ;)
Shielded clamps are all we are using even when we install no-hub cast iron underground nowadays!
|
|
 |
Uber Member
|
|
Mar 13, 2013, 01:25 PM
|
|
Guess we're a bit backward here in GA, Very uncommon to find shielded clamps buried in concrete, or at least that is what I was assuming would happen.
|
|
 |
Senior Plumbing Expert
|
|
Mar 13, 2013, 02:04 PM
|
|
Not to be a smart-alec, but GA IPC 2006 states that mechancial joints with elastomeric seals (shielded clamps) are to be used on PVC ONLY in underground applications (unless transitioning from one material (EX.: copper) to a newer material (EX.: PVC) above ground... how's that for interesting?
In my area for residential applications, we are only allowed one transition clamp (ex.: PVC x cast iron clamp)... if we need 2 of these we MUST repipe all the old work over to NEW PVC up to and through the roof if we pulled a permit! UGH! Commercially, of course, we can use unlimited elastomeric mechanical joints.
Of interest, of course, is that in repair work almost everyone uses multiple clamps, but they are NOT supposed to according to most code books I have read up on!
Anyway, shielded clamps are code approved and really are the easiest to work with in underground applications!
Thanks for working through it with me, Brian!
Mark
|
|
 |
Uber Member
|
|
Mar 13, 2013, 02:54 PM
|
|
HMMM. Well, they just built 42 homes in my neighborhood and 100% of them are solvent cemented DWV drain systems, never saw a shielded one in new construction. Maybe repair and I have used them for PVC/ Cast Iron connections. Oh well, another iota of knowledge.
|
|
 |
Senior Plumbing Expert
|
|
Mar 13, 2013, 04:03 PM
|
|
No no... please don't get me wrong here! PVC should definitely be solvent welded above and below ground whenever possible. In repair work or when adding a branch drain line to an existing drain line like in this case, however, shielded clamps are the way they go underground, but above ground the slip coupling you mentioned earlier is the preferred method, for sure!
Thanks again!
|
|
 |
New Member
|
|
Mar 14, 2013, 05:32 PM
|
|
Thanks guys ,you were all a big help. Now I can proceed with confidence. Tjd5068
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
How to install a pvc 4" wye in a 4" vertical cast iron stack?
[ 2 Answers ]
I need to install a connection in the cast iron stack to accommodate a 2" washer drain. I was thinking about supporting the stack, cutting a section out and installing a 4" pvc wye to run my drain pipe to, which is about 14' away.
How can I install pvc pipes in a concrete slab?
[ 13 Answers ]
I want to cut a 30mm deep channel (about 300mm long) into a 120mm thick concrete slab. Can I do this without compromising the structural integrity of the slab? The slab is elevated, It is in the laundry and is about 50mm from three of the room's walls.
Thanks.
Add a PVC wye to a 4" cast iron soil pipe
[ 3 Answers ]
I have to add a 2 inch line to an existing underground 4" buried cast iron soil pipe. I can follow the shielded coupling of a PVC wye. My question is, how do you clean up the lumpy cast iron pipe so that the perfectly round and smooth coupling actually makes a sealable joint?
View more questions
Search
|