    How to install a pvc 4" wye in a 4" vertical cast iron stack?
    I need to install a connection in the cast iron stack to accommodate a 2" washer drain. I was thinking about supporting the stack, cutting a section out and installing a 4" pvc wye to run my drain pipe to, which is about 14' away.
    joypulv's Avatar
    joypulv Posts: 21,591, Reputation: 2941
    current pert
     
    #2

    Feb 20, 2013, 06:30 AM
    Sure it will work, with a min 1" slope per 4'.
    But code where you are might limit the distance from stand pipe to stack (3'?), plus whether you can put PVC under a vertical run of cast iron. But people do it anyway.
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #3

    Feb 20, 2013, 05:30 PM
    Hi Dmcclain52

    As Joypulv pointed out you can't insert a PVC wye fitting into the middle of a vertical cast iron stack. As mentioned, people do it (using shielded clamps), but not plumbers... ;)

    Here, you would be much better off supporting the cast iron stack using RISER CLAMPS (see image) and then cut in a cast iron no-hub wye fitting (only available at a local plumbing supply store)... use shielded clamps to secure a water/gas-tight installation (see image).

    After you get the cast iron fitting installed you'll need to transition from cast iron to PVC. This can be done using the cast iron wye if you get a wye with a tapped (threaded) branch on the wye fitting, or you could also accomplish this using a shielded cast iron x pvc transition clamp...

    After that, you will also need to consider how it is that you plan to VENT the washing machine drain... ABSOLUTELY required to keep sewer gasses from escaping into your home, OK?

    Care to discuss all this more just let us know.

    Mark
    Attached Images
        

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Add a PVC wye to a 4" cast iron soil pipe [ 3 Answers ]

I have to add a 2 inch line to an existing underground 4" buried cast iron soil pipe. I can follow the shielded coupling of a PVC wye. My question is, how do you clean up the lumpy cast iron pipe so that the perfectly round and smooth coupling actually makes a sealable joint?

Tap into 4" cast iron waste line with 2" pvc [ 1 Answers ]

I want to add a sink in a dental lab as simply as possible. Can I cut a hole in an existing 4" cast iron waste line, fit 2" pvc to the opening and seal it with some kind of resin or wrap? Thank You, Vinny

Tub Drain -- 1 1/2"pvc to 4" cast iron with hub [ 12 Answers ]

Hi . . . I'm replacing my old cast iron tub with a whirlpool tub. The old drain was a 1 1/2" brass tube tucked into a 4" cast iron drain pipe (with hub), packed with what might be oakum. The seal was fibrous and waxy when I cleaned out the drain, and that's not MY hair :) What's the best way...

Replace 1.5" galvanized steel (male threads) to 4" cast iron stack [ 1 Answers ]

I need to replace a drain line from an old double cast iron kitchen sink. The existing pipe is 1.5" galvanized steel which threads directly into female threads on a 4" cast iron stack. The male threads of the galvanized pipe broke off in the cast iron. I'm guessing the easiest solution is to...

Adding a PVC "Y" to a underground Cast iron pipe [ 1 Answers ]

I have a house built in 1962. The cast iron waste pipe runs under the concrete slab in the basement. I have already dug and confirmed the location I want to cut a section out of the pipe and install a "Y" connector and run new plastic waste pipes to a new bath. I have seen PVC connectors that...


View more questions Search