    30 amp to 15 amp receptacle
    I want to change a 220 outlet with 10 gage wire to a 110 outlet on a 15 amp breaker. I'm changing from an electric range to a gas range and only need 110V/15amp and it would be nice not to have to pull new wire.

    Jim
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Dec 18, 2012, 06:34 AM
    You should have 2 hots and a ground. Convert one of the hots to a neutral and mark it as such. You will need to pigtail 14 AWG for the new outlet since you will never get 10 under a screw on an outlet. BTW today's power is 240 and 120. Cover the extra hole in the box with a fill plate -HD carries them. Be careful re -routing in the box.
    creahands's Avatar
    creahands Posts: 2,854, Reputation: 195
    Ultra Member
     
    #3

    Dec 18, 2012, 06:35 AM
    There is no problem using a larger wire then the minimum called for for circuit.

    If old cable is three wire use black as hot, white as neutral and tape off red at both ends.

    Chuck
    jimbosox's Avatar
    jimbosox Posts: 2, Reputation: 1
    New Member
     
    #4

    Dec 18, 2012, 06:46 AM
    Thanks a bunch for the fast replys !
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #5

    Dec 18, 2012, 06:25 PM
    If one of the hot wire is black and the other is white, no problem.

    However, if the second conductor is anything but white or gray, you can not retask the conductor as a Neutral conductor, The Neutral conductor must be gray or white.

    If you were using a #6 AWG conductor or larger, then you would be allowed to retask the conductor.
    Kyle_in_rure's Avatar
    Kyle_in_rure Posts: 341, Reputation: 10
    Full Member
     
    #6

    Dec 18, 2012, 07:40 PM
    Be careful fitting those 10 AWG wires under the receptacle screws, #10 is so thick it's sometimes hard to do.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

20 amp and 15 amp receptacle on same 20 amp circuit [ 4 Answers ]

Is it safe and within code to install a 20 amp receptacle and a 15 amp receptacle on the same 20 amp circuit using 12/2 wiring throughout? And If it is okay, does it matter if the 20 amp receptacle is end or middle of the line? Thanks, K

Can you use a 15 amp receptacle on 20 amp breaker [ 2 Answers ]

Can you use 15 amp outlet plug on a 20 amp breaker

15 amp GFI receptacle on a 20 amp circuit [ 1 Answers ]

Can a 15 amp GFI receptacle be used on a 20 amp circuit wired with 12 gage wire? I understand that it is okay to use 15 amp receptacles and switches on 20 amp circuit breakers wired with 12 gage wire.

15 amp receptacle with a 20 amp feed through [ 2 Answers ]

What does it mean when a GFCI receptacle is rated 15 amps with a 20 amp feed through?


View more questions Search