    Hooking up a GFI to Jacuzzi 220 v olt 40 amp, why can't I use a Circuit breaker in it's place?
    Email [email protected]
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 11, 2012, 03:16 PM
    A hot tub is required by the National Electric Code to be protected by a ground fault protection device.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #3

    Dec 11, 2012, 08:15 PM
    TK has given you te correct but brief answer, it's the law. The law, the code was created to protect people from electric shock and death in wet areas. GFCI in wet areas and ARC faults in bedrooms, it's the law made to keep you alive. If you go to Home Depot or Menards they sell a special package deal for hot tubs, everything you need in one box.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #4

    Dec 11, 2012, 09:13 PM
    Circuit breakers only work with overloaded circuits. GFCI on the other hand have no relation to overload, they react to imbalance, particularly noted with a shortcoming in the ground part of the system, and trip. Saving money by using a breaker alone is foolhardy when it comes to water.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #5

    Dec 12, 2012, 06:08 AM
    Do the installation instructions require it?
    If so... NEC 110.3(B) requires it as well or the owner will accept
    All liability for damage or injury.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Dec 12, 2012, 08:38 AM
    A circuit breaker is designed to "Open" in the event of an overcurrent (high amperage) on the branch circuit.

    A "GFCI" gevice is designed to protect people from getting themselves killed. It reacts when it detects a .6 difference in amperage between the hot and neutral of the connected circuit.

    You can get a "GFCI" breaker, but that means that any fault detection that trips the GFCI circuit inside the breaker will make you walk to the breaker to reset it.

    Clear as mud?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Which trips first a GFI or circuit breaker [ 1 Answers ]

I have an outside set of outlets all hooked up with GFI's. The last on the run is used for the small pond pump. It runs for about 3 days then throws the circuit breaker. If I hook the pond pump to my front yard outlet, it works forever. I didn't reset the last GFI and ran the pump off my second...

Installing GFI circuit breaker [ 1 Answers ]

I have installed a GFI circuit breaker and connected it to a simple circuit--a plug. When I plug anything into the plug, it trips the GFI interrupt. The circuit tests successfully, and works well if I replace that breaker with a non-GFI breaker. The GFI breaker is set up the same way as a...

New GFI Circuit Breaker trips [ 2 Answers ]

I just installed a GFI circuit from my breaker box and am faulting. I'm confident that I installed the breaker correctly with the breaker pigtail going to the power return bus and the black and white wires going to the correct terminals. If I operate the breaker without the earth grd connected it...

Replacing a circuit breaker with a GFI breaker- q on neutrals [ 1 Answers ]

In process on installing withquestion on neutral wires. Do you take the neutrals out of the in the main panel neutral and put them in into the breaker where its labelled "load neutral terminal" and only have the neutral "pig tail" to the panel neutral bar? Thanks!