    Installing GFI circuit breaker
    I have installed a GFI circuit breaker and connected it to a simple circuit--a plug. When I plug anything into the plug, it trips the GFI interrupt. The circuit tests successfully, and works well if I replace that breaker with a non-GFI breaker.
    The GFI breaker is set up the same way as a non-GFI model, with the exception that the pigtail is in the grounding bar,
    What am I missing?

    Gerry Stoner
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Apr 27, 2008, 11:12 AM
    Ground fault neutral pigtail should go to neutral bar, but should have operated in ground even though it is wrong. Would correct.
    The hot from GFI breaker goes to receptacle Hot, The Neutral to the receptacle connects to the other screw on the GFI breaker, If receptacle neutral is on neutral or ground bar, it will trip, equal load must be maintained on protected hot and neutral.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Theory of vacuum Circuit Breaker & sf6 circuit breaker [ 15 Answers ]

I want to know about the basic Theory of vacuum Circuit Breaker & sf6 circuit breaker

Replacing Circuit Breaker with Higher AMP Breaker [ 8 Answers ]

Excuse me, I did look at the code book as is suggested in your Sticky. The NFPA may answer this question, but I am not knowledgeable enough to recognize it: Our offices are upstairs in an older (renovated home) building with modern wiring. We have 4 computers, 3 printers, and miscellaneous with...

Installing a circuit breaker in an existing box; alternative forms of electricity [ 18 Answers ]

Hello: I have a Sears Craftsman 6hp 150 psi 33 gallon compressor. Electrical measurements are 120v/15amps - basically meaning it could run on normal household current. However, when I start it up, after about 3 seconds, it shuts off. I tried using the dedicated outlets in my apartment,...

Circuit breaker [ 3 Answers ]

Circuit breaker will not reset

Replacing a circuit breaker with a GFI breaker- q on neutrals [ 1 Answers ]

In process on installing withquestion on neutral wires. Do you take the neutrals out of the in the main panel neutral and put them in into the breaker where its labelled "load neutral terminal" and only have the neutral "pig tail" to the panel neutral bar? Thanks!


View more questions Search