    Trouble shooting gas furnace flame roll out
    I have a Goodman furnace that is 12 years old that is having a flame roll out on the first chamber intermittently. I have checked stack for blockage, what should I check next
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #2

    Dec 8, 2012, 12:08 PM
    Check gas pressures. Also check to make sure orifices are clear. Next, a CO test should be done (could have a crack in the heat exchanger,, worst case senerio). You may also have a partially blocked heat exchanger. Flame rollout is a very serious issue, so if you can't find the cause, you should call in a tech. Don't be surprised to find that a new furnace may be suggested.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Evcon gas furnace trouble shooting [ 2 Answers ]

The indicator lights blink 3 times, which says that the centrifugal switch is stuck open. I have located the centrifugal switch, and with power off, have gently tapped to free, which apparently has not worked. This is an Evcon propane gas furnace. I have the thermostat all the way up, power is...

Rheem gas furnace trouble shooting codes? [ 0 Answers ]

Is there a manual of trouble shooting codes for Model# RGDG-15EARJR - THE FURNACE IS DOING A DOUBLE FLASH AND WON'T IGNITE I can be emailed at [email protected]

Goodman furnace with 3 blinking lights and furnace has flame roll back [ 7 Answers ]

I have a GMNT-080-4B Some times I get a 3 blink light issue and then when it starts it has a flame roll back. Also I have to change the ignitor every year. Any help would be great

Trouble shooting 95% Goodman gas furnace? [ 0 Answers ]

GMH950904CXA. When the blower comes on the burners start to afed like the wind is blowing on them and the roll out switch shuts down the 24 volt's. Checked for CO found 0 PPM in house at regesters. Furnace is three yr's old in horrizonal position. Never seen this before. Any Ideas.

Trouble shooting-Centurion gas furnace [ 0 Answers ]

Have rheem centurion gas furnace- lights- but won't stay lit- any suggestions? Important #'s:letters: RGPJ1ONBRJR And EB5D307F449900215... any help would be greatly appreciated. Brrrrrrr.


View more questions Search