    50AMP Breaker Selection for Generator Power Inlet
    I am buying a DuroMax XP10000E 10,000 Watt gas Generator which has a 120v/240v 50 Amp Heavy Duty Outlet (NEMA 14-50 3 Pole 4 Wire).

    I will install a 50-Amp Power Inlet Box just inside the garage door & connect the generator to the inlet with a 50-Amp (10 Foot) Generator Power Cord w/ Straight Blade.

    I will connect the 50-Amp Power Inlet Box to the main panel in the basement by running a 6/3 from the inlet box to the main panel.

    Since the neutral & ground Bus is shared, it won’t matter which side of the panel’s Bus the neutral & ground is connected to.

    Since each side of the panel is separate and must be energized individually, I need to know which breaker do I use?

    Options may include:

    1. Using 2 - 50AMP double pole breakers & feeding only one positive (red or black) to each of the breakers, one on each side of the panel.
    2. Using 2 – 25AMP single pole breakers & feeding one positive (red or black) to each of the breakers, one on each side of the panel.
    3. Other – explain.

    In advance, thanks for your help.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Nov 8, 2012, 04:07 AM
    There is no positive and negative in AC wiring.

    You need a 50A 2-pole breaker. That's it.

    You do not add up the poles, meaning a 2-pole 25A breaker is not a 50A breaker.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #3

    Nov 9, 2012, 05:20 AM
    As stated you are proposing an illegal installation. You need a transfer switch or an interlock mechanism. You aren't providing any protection for backfeeding the line. Just what are you thinking?
    Kyle_in_rure's Avatar
    Kyle_in_rure Posts: 341, Reputation: 10
    Full Member
     
    #4

    Nov 11, 2012, 08:51 PM
    You just need a 2-pole 50 amp breaker, as others have said. Red to one side, black to the other, white to neutral bus, and ground wire to ground bus.

    You really should install an interlock kit to prevent accidental line backfeeding. Besides being illegal, you could kill a lineman or damage your generator depending on the circumstances. You may remember to turn off the main breaker, but others in the future may not. They are relatively easy to install, might want to look them up.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

220v spa question: With a 50amp breaker box outside, what amp breaker is okay inside? [ 1 Answers ]

Currently, I have a 50amp GFCI breaker on the side of my house, getting juice from a 60amp breaker inside the house at the main breaker box. Is this okay or not? I have #8 wire I was going to run between the two... Here is from the electrical section of the manual: "If you have purchased a...

Adding a 50amp breaker to my 100amp service. [ 1 Answers ]

Actually, I am not sure what the incoming service is. The Master Circuit Breaker for the box is 100amp. I want to put in an electric oven/range. It requires a 50amp breaker be used. My service panel is full, but I do have a 30 amp breaker that I can pull out.(It is for baseboard heaters that...

How to connect a power generator to the circuit breaker [ 1 Answers ]

How to connect the power generator to the circuit breaker

Generator inlet plug - 50amp versus 30amp [ 2 Answers ]

I have a generator with a continuous run of 7000 watts and a surge of 8750 watts. I bought a manual transfer switch to install in the house. It has a peak of 12,500 watts. The inlet plug is an Nema L14-50 and is incompatible with my generator as it has a Nema L14-30 plug. My question is, can I...


View more questions Search