For 240v with voltage drop limited to 2.95% you will want three (copper) 600MCM conductors and a 3/0 ground
(and a tugger)
1 conductors per phase utilizing a #600 Copper conductor will limit the voltage drop to 2.95% or less when supplying 208.0 amps for 450 feet on a 240 volt system.
For Engineering Information Only:
420.0 Amps Rated ampacity of selected conductor
0.023 Ohms Resistance (Ohms per 1000 feet)
0.039 Ohms Reactance (Ohms per 1000 feet)
7.199999999999999 volts maximum allowable voltage drop at 3%
7.058. Actual voltage drop loss at 2.95% for the circuit
0.9 Power Factor
In addition... what type of load or loads are intended to be supplied?
The amount of voltage drop is dependent on the amount of load. Also if
This is a motor load or loads you must be careful of the inrush. This will limit the
Amount of load you can connect to the generator...