    What size wire/cable is recommended to use in pvc conduit from a 50 kw generator with a run of 450'? Any help will be appreciated. Thanks.
  • Oct 23, 2012, 02:31 AM
    tkrussell
    What voltage?
  • Oct 27, 2012, 10:52 AM
    shuntripper
    For 240v with voltage drop limited to 2.95% you will want three (copper) 600MCM conductors and a 3/0 ground
    (and a tugger)

    1 conductors per phase utilizing a #600 Copper conductor will limit the voltage drop to 2.95% or less when supplying 208.0 amps for 450 feet on a 240 volt system.
    For Engineering Information Only:
    420.0 Amps Rated ampacity of selected conductor
    0.023 Ohms Resistance (Ohms per 1000 feet)
    0.039 Ohms Reactance (Ohms per 1000 feet)
    7.199999999999999 volts maximum allowable voltage drop at 3%
    7.058. Actual voltage drop loss at 2.95% for the circuit
    0.9 Power Factor
  • Oct 27, 2012, 03:47 PM
    stanfortyman
    Quote:

    7.199999999999999 volts maximum allowable voltage drop at 3%
    There is no 'allowable' voltage drop. Countering voltage drop is a suggestion under the NEC, not a requirement.
  • Oct 29, 2012, 03:44 AM
    hfcarson
    In addition... what type of load or loads are intended to be supplied?
    The amount of voltage drop is dependent on the amount of load. Also if
    This is a motor load or loads you must be careful of the inrush. This will limit the
    Amount of load you can connect to the generator...