    tnsser's Avatar
    tnsser Posts: 5, Reputation: 1
    New Member
     
    #1

    Oct 15, 2012, 05:43 PM
    Will 6 be enough for a 240v 50 feet?
    I am running 240 for a shop air compressor. It is a single phase. I need about 50 ft of wire to make the run. What size wire? I
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Oct 15, 2012, 06:05 PM
    What is the load?
    tnsser's Avatar
    tnsser Posts: 5, Reputation: 1
    New Member
     
    #3

    Oct 15, 2012, 07:21 PM
    45 on start up
    tnsser's Avatar
    tnsser Posts: 5, Reputation: 1
    New Member
     
    #4

    Oct 15, 2012, 07:22 PM
    14.7 amps
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Oct 16, 2012, 03:47 AM
    #12 on a 20A or 25A breaker.
    You can even use #14, but I typically don't wire things like tools, machines, etc, with less than #12.

    Who told you you needed #6?
    tnsser's Avatar
    tnsser Posts: 5, Reputation: 1
    New Member
     
    #7

    Oct 16, 2012, 06:40 AM
    Nobody I just thought I needed a 60 amp breaker to run the compressor. I was told the compressor will pull 45 amps at start up.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #8

    Oct 16, 2012, 08:13 AM
    Not necessarily. Motors are a strange breed of animal. All motors have an in-rush amperage that can be quite high, but not adversley effect the breaker. The wire from the breaker to the motor should be sized at 125%.

    For example, you need to get the full load amperage required by the motor. You can get that from the tables at the end of NEC Article 430 if that is not on the electrical specs with the motor. Then multiply the FLC by 1.25 to get your operating amperage.

    14.7 FLC X 1.25 = 18.4 (rounded up)

    A 12 AWG wire is listed for up to 20 amps. So as instructed earlier, it is safe for use.

    Turn your attenion to the breaker, you need to size the breaker or fuse for this circuit so that it can handle the inrush current without tripping the breaker or opening the fuse. THis information is also in Article 430. Sorry but I don't have my copy of the NEC handy at the moment so I cannot give you info on the correct size.for the fuse or breaker.

    Check the electrical specs that came with the unit, they should have the information you need there.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #9

    Oct 16, 2012, 03:49 PM
    Nobody I just thought I needed a 60 amp breaker to run the compressor. I was told the compressor will pull 45 amps at start up.
    No offense, but this is a perfect example of why you should have a good idea of what you are doing before you do it.

    I'm glad you are asking now and not after.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

240v transformer to 120,208,240v what wires [ 3 Answers ]

I'm replacing a 240v transformer in a split heat/cooling unit. The old trans has 4 prongs 2 load 2 line the new one has two secondary and 4 primary wires what wires do I use for primary?

A triangle has a base 12 feet long and an altitude 8 feet high. Find the area of the [ 1 Answers ]

A triangle has a base 12 feet long and an altitude 8 feet high. Find the area of the largest rectangle that can be inscribed in the triangle so that the base of the rectangle falls on the base of the triangle.

We would like to put a 240v pannel or sub box 160 feet from our main. [ 1 Answers ]

240 v sub box/panel 160 feet from main, what size and kind of wire or romex/ conduit is aproved?

240v breakers forces 240v through 1 leg? [ 2 Answers ]

My single phase power panel works fine, as long as all of the 240v breakers are off. Service into the main breaker reads a steady 120v on each leg from the transformer, and 240v across both legs. But, when I flip on ANY of the 240 breakers, all 240v jumps to one leg of the panel (for both single...

What will it cost to tile a kitchen floor that is 12 feet wide by 20 feet long if the [ 5 Answers ]

What will it cost to tile a kitchen floor that is 12 feet wide by 20 feet long if the tile cost $8.91 per square yard?


View more questions Search