    My single phase power panel works fine, as long as all of the 240v breakers are off. Service into the main breaker reads a steady 120v on each leg from the transformer, and 240v across both legs. But, when I flip on ANY of the 240 breakers, all 240v jumps to one leg of the panel (for both single pole and double pole breakers), and the other leg goes dead. This is causing many problems throughout the entire system... 240v to one side, and 0v to the other for all circuits. As you can imagine, we are having multiple overvoltage/dead circuit problems. As long as the 240v breakers are off, the system works fine.

    After disconnecting everything in the panel, the continuity readings all come back clean, indicating that there are no crossed or broken wires.

    Any suggestions or answers??
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Sep 5, 2010, 08:49 AM

    Sounds like a neutral problem, Measure between each hotleg and neutral(should be 120 volts) and between the 2 hotlegs(should be 240 volts).
    Start at the Disconnect, then lugs on panel, then out of breakers last.
    Could be a Power company problem.
    Neighbors having problems?
    Take a visual at your overhead wires and out to pole, an look at the bare wire for a broken connection. You can sometimes see the problem.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #3

    Sep 5, 2010, 12:06 PM

    Come back clean? You mean open, not shorted, right? If it's a system wide problem you could have an open neutral... that would give you the same reading. You said ANY of the breakers? But all of your 120v outlets work on both sides of the panel.. unless you turn on a dbl pole... is that correct? I'm wondering if the neutral / ground bond isn't completing the circuit when the dbls are off. Might be time to call an electrician. Do as Strat suggested first, check with the neighbors and do the troubleshooting as long as you have the experience to do it.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

240v transformer to 120,208,240v what wires [ 3 Answers ]

I'm replacing a 240v transformer in a split heat/cooling unit. The old trans has 4 prongs 2 load 2 line the new one has two secondary and 4 primary wires what wires do I use for primary?

240v basebord heater, and breakers [ 1 Answers ]

I have 2-8ft 2000 watt (8.3 amps each, total 16.6 amps) heaters wired to a 20 amp breaker with no problems. But since each of the heaters are in different rooms, and one room is bigger (where the thermastat is) I need to change this one baseboard to a 2500 watt 8 ft 10.1 amp unit to equal out the...

Single pole breakers for 240v heater? [ 2 Answers ]

Thanks in advance for any help.. I am trying to set up new 240 v baseboard heating in my attic My questions is can I put it through 2 different single pole breakers - each for every phase? Heater = 240v / 1500w breakers = 15A And what can be wrong? (technically - this is not a code...

82v on one leg of 240v at breaker box [ 1 Answers ]

Neighbor complained of 120v window A/C not working and dim lamps on same circuit in old mobile home. Check of circuit revealed 82v on 120v circuit. Further check of incoming line showed 82v on one leg of service in breaker box (resulting in 82v on the affected bus bar). Disconnect box at service...

Connecting 240v heater to 2 - 1 pole breakers [ 2 Answers ]

I have 2 - 15amp tandem breakers - both are 1 pole. I know that normally you would use a 2 pole breaker to create a 240v feed to the heater. However, if I connect my 12-2 wire to the 2 different breakers, I get 240v and my heater works correctly. Is there any problem to doing this rather than...


View more questions Search