    Service cable size for a polebarn?
    I am trying to buy direct burial cable for a 240 volt service from my house to my polebarn. The barn is just for residential use & the biggest thing I plan to use is a 2 post lift which is 30 amp. I have a 200amp house service that I have a 100amp 2 pole breaker in that I will run the cable from. I plan to run direct buriable cable to a 100amp service panel in my polebarn. The distance totals 270ft from house to polebarn. I looked at copper wire (2 x 1/0 with a #6 neutral return) at nearly $1,900 I decided to look at aluminum instead. I used online calculators to find that I need 2/0 for aluminum but am not sure on the return neutral size needed? I found a cable bundled together 2/0, 2/0 & #1 called "converse underground secondary distrbution cable", is this OK or should I use separate cables? It totals only $403! I am aware that I need to use a dieletric paste to avoid corrosion, is there anything else I need to know about using aluminum instead of copper? Thanks.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Sep 5, 2012, 06:18 AM
    You will need a 4 wire cable or system.

    If you can find 4 wire #2/0 aluminum URD cable, it would suffice.

    URD cable is rated for direct burial, will need conduit sleeve for physical protection where exposed out of ground.

    Most aluminum wire nowadays does not need anit-oxidant compound uses at connections and terminals, but need to check the manufacturers datasheet. I use it anyway, if needed or not.
    slaptop's Avatar
    slaptop Posts: 7, Reputation: 1
    New Member
     
    #3

    Sep 5, 2012, 09:48 AM
    I am confused, why would I need 4 x 2/0? I was planning on 2 hot wires at 2/0, plus a neutral return at either #6 copper or whatever that equates to in aluminum. Plus a separate ground wire to the ground rod at the polebarn. Thanks
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Sep 5, 2012, 12:07 PM
    If ungrounded (live) conductors are increased to deal with voltage drop all conductors must be increased proportionally.

    If you find the URD I mentioned, you will find that it is 2 -#2/0, plus probably a #1 for the neutral, and a #4 for the equipment ground. I am guessing the reduced wire sizes, but they are smaller than the live wires.
    slaptop's Avatar
    slaptop Posts: 7, Reputation: 1
    New Member
     
    #5

    Sep 5, 2012, 01:58 PM
    Quote Originally Posted by tkrussell View Post
    If ungrounded (live) conductors are increased to deal with voltage drop all conductors must be increased proportionally.

    If you find the URD I mentioned, you will find that it is 2 -#2/0, plus probably a #1 for the neutral, and a #4 for the equipment ground. I am guessing the the reduced wire sizes, but they are smaller than the live wires.

    I was just planning to run a wire to a ground rod outside the polebarn. I already have a ground rod for the house panel. Are you saying I have to link the house ground to the polebarn also? Seems a long distance to run a ground wire? Thanks
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Sep 6, 2012, 02:31 AM
    3 wire feeders to separate structures are no longer allowed. You must run an equipment grounding conductor and drive a rod at the barn.
    slaptop's Avatar
    slaptop Posts: 7, Reputation: 1
    New Member
     
    #7

    Sep 6, 2012, 10:32 AM
    Quote Originally Posted by tkrussell View Post
    3 wire feeders to separate structures are no longer allowed. You must run an equipment grounding conductor and drive a rod at the barn.
    Many thanks, I had seen this on a schematic but was not sure. I'll work out the correct sizes & price them out. Thanks for your help.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Cable requirements for power to a polebarn [ 5 Answers ]

I have a new polebarn 270ft from my house. I need to run 100amp 220 volt service to it do that I can power a 2 post vehicle lift, some lighting & general 120volt outlets. I plan to breaker out of my houses 200amp panel with 100 amp breaker. Run cable in conduit to a 100 amp service panel in the...

Load Center service cable size [ 11 Answers ]

Installed a 125 Amp main breaker load center 190' from main. I Have already roughted in part of the run w/ 2" PVC conduit. Plan to run full length in 2". I estimate that approx. 80-90 Amps would be max load during normal usage. Called a number suppliers about aluminum cable and got...

Service entrance cable (alum) size for a 100 amp service at 186 feet for a garage [ 1 Answers ]

The garage is 186' from the service at the house. I wanted to make sure the voltage drop would not cause a problem.

Service Cable size/characteristics [ 1 Answers ]

Wish to run 100 amp service from a sub panel on the outside of my home to a pier where will have sub panel at end of pier. Also need to run 60 amp to another outside location. Cables will be buried. What type/size cable should be used.


View more questions Search