    Hot tub wire size
    I am installing the electrical service for a new hot tub. I have done this before and am familiar with safety issues, grounding, gfic requirements, convenience outlet requirement within 10', etc. The installation instructions state that I should use #8 AWG for runs up to 50', and #6 AWG for runs over 50'. I will install a 50A breaker in my house elec service panel and run a line to a gfic disconnect box; then come out of the gfic box to the hot tub. The distance from my electrical service panel to the gfic disconnect box will be 40', and the distance from the gfic disconnect box to the hot tub will be about another 30'. Though this is a total of 80' (well over the 50' maximum), do I need to use #6 AWG wire for both runs, or since I am breaking the total run legnth with two runs under 50', can I use #8 AWG wire for both runs? The town that I live in does not have local elec code or a code enforcement officer. They fall back on NEC. Thank you.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Aug 11, 2012, 03:12 PM
    #6 the whole way.
    And if you are using any NM cable inside the house you'd need #6 anyway.
    rle26's Avatar
    rle26 Posts: 3, Reputation: 1
    New Member
     
    #3

    Aug 12, 2012, 06:59 AM
    Thank you stanfortyman. Very helpful, especially the additional info re: using #6 AWG for NM cable (I did not know that I must upgrade to #6 for NM - even if the run was under 50'). Since I did plan to use sheathed NM cable for the run through the basement from the panel to the GFIC disconnect, that added info is very, very helpful. I will convert to individual stranded #6 AWG in 1" pvc conduit from the outdoor GFIC box to the tub.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Aug 12, 2012, 07:14 AM
    The reason is that #6 NM cable is rated differently that THHN/THWN conductors in conduit.
    rle26's Avatar
    rle26 Posts: 3, Reputation: 1
    New Member
     
    #5

    Aug 12, 2012, 08:26 AM
    Quote Originally Posted by stanfortyman View Post
    The reason is that #6 NM cable is rated differently that THHN/THWN conductors in conduit.
    Got it; Thanks again stanfortyman!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How can I use an older 3 wire 220 circuit for a 4 wire hot tub [ 6 Answers ]

Can I somehow use an existing 3 wire 220 volt circuit to power a 4 wire hot tub? Running a new 4 wire circuit back to the main panel will be long and difficult. I have nearby access to an old 3 wire sub panel once used for an air conditioner. This original circuit is missng the ground wire.

What size breaker for hot tub [ 3 Answers ]

HI All I live in a condo . Our hottub heater conections got loose and burned up the insides of the control box. The heater is 15 plus years old so we bought a new unit. We replaced the wires from the gfci too the control box on top of the heater with #6wire My question is if I'm...

Hot tub wiring 4 wire 3 wire [ 15 Answers ]

I have a 4 wire hot tub and have it wired to my 4 wire 60 amp gfci box outside, and it then goes into my basement where there is no 4 wire service. Do I connect the ground and neutral to the same location in the basement? :confused:


View more questions Search