How can I use an older 3 wire 220 circuit for a 4 wire hot tub
Can I somehow use an existing 3 wire 220 volt circuit to power a 4 wire hot tub? Running a new 4 wire circuit back to the main panel will be long and difficult. I have nearby access to an old 3 wire sub panel once used for an air conditioner. This original circuit is missng the ground wire.
|
|
 |
Ultra Member
|
|
May 29, 2010, 07:14 PM
|
|
Dought the wire is big enough to work on the tub
|
|
 |
Electrical & Lighting Expert
|
|
May 29, 2010, 07:18 PM
|
|
You MUST have a dedicated ground wire AND a neutral for a 4-wire feed, and in most instances the ground MUST also be insulated.
You absolutely cannot use a 3-wire feeder for a 4-wire hot tub.
Also, Josh is right. What size is the old wire and what size is needed for the tub? It is doubtful that an old A/C line is that big.
|
|
 |
New Member
|
|
May 29, 2010, 07:32 PM
|
|
The wires are big enough, 6 AWG at least, originally used for either a central A/C unit or heat pump. That shouldn't be a problem Could I run a separate ground wire either through the attic or crawl space?
|
|
 |
Uber Member
|
|
May 30, 2010, 04:56 AM
|
|
Sorry, but no,
 Originally Posted by TennBrian
Could I run a seperate ground wire either through the attic or crawl space?
A new 4 wire cable must be installed.
|
|
 |
New Member
|
|
May 30, 2010, 06:06 AM
|
|
I apologize for pressing the point, but what difference can it make if the ground wire makes the trip to the sub panel a different way, as long as it's properly connected to both panels? I know it's not the most professional of installations, but I'm trying to avoid making a long run of expensive cable through and under concrete.
I suppose, ultimately, this conversation all boils down to following the code.
|
|
 |
Uber Member
|
|
May 30, 2010, 08:22 AM
|
|
Exactly,
 Originally Posted by TennBrian
I suppose, ultimately, this conversation all boils down to following the code.
I hear what your saying, and I understand the concept, but I cannot suggest or recommend a practice that specifically is not allowed by Code.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Black wire red wire and white wire spliced to 10/3 on a 220 circuit
[ 25 Answers ]
I have installed a disconnect between my dryer receptable and a tanning bed. I want to splice the 10/3 box wire to the existing 220 wiring at the dryer.
Dryer= red, black, white and bare ground wires
10/3 wire= black, white, and bare ground
How do I splice these to allow the disconnect box to...
Older 220 volt wire
[ 13 Answers ]
I have an older 220v wire with only 3 wires... 2 hot and 1 ground/neutral (bare). I need to connect (splice) it to a newer 220v wire with 4 wires... 2 hot, 1 neutral (white), and a ground (bare).
And older I mean less than 15 years old.
View more questions
Search
|