    baseboard electric thermostats
    I am wiring 3 baseboard heaters 2 1500w in series attached to one thermostat and 1 1500w heater on the other thermostat. I was planning on having them all on the same 30amp circuit but the thermostats (digital programmable) are rated for 16.x amps. Is it OK to have the thermostats on a 30amp circuit? They would not have 30amps going across normally them but if something went bad I suppose they could.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Jul 31, 2012, 06:37 AM
    That is fine. The thermostats need to be rated for what they are controlling.
    The 3000 watt load is only 12.5A.
    missfittsx's Avatar
    missfittsx Posts: 3, Reputation: 1
    New Member
     
    #3

    Jul 31, 2012, 08:30 AM
    Just seems like if a heater went bad and started drawing a much larger current the thermostat would not be able to handle the current draw and the breaker would not trip.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Jul 31, 2012, 08:44 AM
    How can a heater go bad and draw more current?
    missfittsx's Avatar
    missfittsx Posts: 3, Reputation: 1
    New Member
     
    #5

    Jul 31, 2012, 08:52 AM
    Not sure how it would since its already getting its heat from resistance. Speaking more hypothetical. Appreciate your help...
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Jul 31, 2012, 08:53 AM
    Well, if there is a problem like an element shorting out the fault current will definitely trip the breaker.
    Nothing can really cause the heater to draw more than it's rating for very long of a time.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

2 baseboard heaters, 2 thermostats [ 5 Answers ]

I have ran a 12/2 up to a point where I want to power two 1500 (240v) watt baseboard heaters each running off a separate thermostat. Each heater will heat a separate room. I have double-pole wall-mount thermostats. Do I split my 12/2 and go to the thermostats or is there another way this should...

Baseboard heater thermostats [ 1 Answers ]

I have removed four (220) baseboard heaters. I shut off breakers to those plugs but still have power at the thermostats. How is this possible?

Replacing 3 wire thermostats for electric baseboard [ 0 Answers ]

We have not been able to replace thermostats with 3 wire type. Lowe's employee told us to buy 4 wire and cut off 1 and install. This is the second time we replaced thermostats in one year. The heat just keeps running. Is it possible we need to replace baseboards or it sounds like we have the...

Thermostats for electrical baseboard heaters [ 1 Answers ]

I have two sets of cables in the wall box. They each have one white wire and one black wire. They are not marked. Only one of the black/white wires that come from one of the cables has power (120volts) the black and white wires from the other cable don't measure any voltage. The thermostat I...

Thermostats for baseboard heat [ 4 Answers ]

We built our house 30 years ago using electric baseboard heat. This is 240 volt electric heat. We would like to change the original thermostats (Mears M7) to progammable digital themostats. Those that we have looked at indicate two models; single pole and double pole. How would I determine which...


View more questions Search