    Is # 4 awg thhn copper big enough for 100 amps
    Can I use # 4 awg thhn copper for 100 amps is it big enough ?
    Lectricman's Avatar
    Lectricman Posts: 2, Reputation: 1
    New Member
     
    #2

    Jul 26, 2012, 06:57 PM
    Use #2awg copper minimum at least in Canada, assume US to be same.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Jul 27, 2012, 02:35 AM
    #3 THHN copper is rated 100 amps, as per Table 310.16 of the 2008 edition National Electric Code for a feeder.

    If this feeder is the service entrance conductors for the service of a dwelling, you may use #4 copper.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Amps for a #6 AWG [ 2 Answers ]

How may amps will a #6 AWG handle?

12 awg thhn on 30 amp overcurrent [ 3 Answers ]

Why can't you use a 30 amp overcurrent device on a 12 awg thhn conductor?

Cost to upgrade from 100 amps to 200 amps and ground [ 4 Answers ]

StanFortyMan has made a lot of sense about my needs in a home with a 100 AMP Service.. I would like to upgrade to 200 amps.. with some ground sockets(or whatever this is called) and put in more sockets... The house is 1300 square feet... does anyone have a guestimate of costs?? Thanks, Annie

AWG size for 40 amps. [ 3 Answers ]

Remodeling kitchen. I now have an oven with 8AWG and a 30 amp breaker. The new oven requires 40 amps. The run is 20 feet. Will the 8 awg do with a 40 amp breaker? Thanks, Shortround3.

Changing from 100 amps to 200 amps [ 1 Answers ]

I have a gas water heater (40 gallon tank). I want to change it to an electric tankless water heater. I have read that I need 200 amps in the house to do this, but currently I have only 100 amps. The outside meter is located only about 25 feet away, but the lines are underground. What is...


View more questions Search