  • Jul 26, 2012, 06:18 PM
    alexandertmg
    Is # 4 awg thhn copper big enough for 100 amps
    Can I use # 4 awg thhn copper for 100 amps is it big enough ?
  • Jul 26, 2012, 06:57 PM
    Lectricman
    Use #2awg copper minimum at least in Canada, assume US to be same.
  • Jul 27, 2012, 02:35 AM
    tkrussell
    #3 THHN copper is rated 100 amps, as per Table 310.16 of the 2008 edition National Electric Code for a feeder.

    If this feeder is the service entrance conductors for the service of a dwelling, you may use #4 copper.