    Venting
    Can I vent my kitchen sink at the floor in the basement
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    Jul 8, 2012, 02:52 PM
    Quote Originally Posted by fireman95 View Post
    can i vent my kitchen sink at the floor in the basement
    No! You would be building a "S" trap which is outlawed. A better solution would be to install a AAV, (air admittance vent) just off the trap. (see image) Good luck, Tom
    Attached Images
     
    fireman95's Avatar
    fireman95 Posts: 3, Reputation: 1
    New Member
     
    #3

    Sep 3, 2012, 05:47 AM
    ihave the double sink that connect togather in my kitchen. And the traps stright down from the pipe were the two connect

    I got a answer for this before,but I did not give enough details ,the venting at the basement floor was very helpful .But I have a double kitchen sink and the pipe rund=s fron one to the other then the trap in my kitchen sink .Where would I put the aav do not have enough room to put it after the trap
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #4

    Sep 3, 2012, 06:08 AM
    the traps stright down from the pipe were the two connect
    Each side of the sink has its own trap? Does the drain come out of the wall or go down into the floor from the traps? Back to you. Tom
    fireman95's Avatar
    fireman95 Posts: 3, Reputation: 1
    New Member
     
    #5

    Sep 3, 2012, 06:57 AM
    Quote Originally Posted by speedball1 View Post
    Each side of the sink has its own trap? Does the drain come out of the wall or go down into the floor from the traps? Back to you. Tom
    One trap for both sinks then goes into the floor
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #6

    Sep 3, 2012, 07:25 AM
    Sorry! You said traps so I assumed a trap for each tub. You do have the room to install a AAV but you will have to replace the elbo going into the floor with a sanitary tee on its back followed by a street ell and 2 45's in the vertical line to connect back, The AAV goes in the tee. Good luck, Tom

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Venting [ 1 Answers ]

Hi.. plumbing code says fall of pipe must not be greater then size of trap. So a 1-1/2 pipe/trap at 1/4 per foot fall needs a vent at 6 feet. Question if I run this pipe 20 feet, do I need more then one vent along the pipe? Every 6 feet?

Venting [ 11 Answers ]

I have a dog running around the neighborhood. She or He looks totally sad and wanting to go home, but can't find their way. NO TAGS! Just a flea collar. It's breaking my heart that I can't help this dog. I opened my garage and the dog was there, looking at me... as if.. am I home? I thought...

Venting Soil Line - Can I use 1 vent for all of my venting needs? [ 8 Answers ]

Hi, I am renovating an old house and have decided to add a master bathroom. I currently have 1 (ea) 2 inch vent pipe penetrating the roof line. I'd like to branch off the single pipe and run several vent pipes off the single one mentioned above to vent two bathrooms, the kitchen sink, and...

Maybe I am just venting, maybe not [ 1 Answers ]

Ugh, so I generally try not to talk about me. Well, you know what I mean, I don't give the personal information about things that really bother me, because generally things don't really bother me. I am so the type to break up with someone if I know a relationship is stagnant and never look back...

Venting Thanks [ 7 Answers ]

Spent last 3 hrs reading threads, trying to answer my questions. Thank you for this site! I am working on new construction. I would like to confirm some things I think I learned on this site. Please answer T/F. If False please fix me. 1 every fixture w/trap needs vented. EX tub lav toilet...


View more questions Search