    Can ser cable be installed in pvc conduit
    Can ser cable run underground in rigid pvc conduit
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jul 8, 2012, 04:29 AM
    Conduit is used to sleeve SER cable for short distances, and will be oversized. To pull SER cable through a conduit system would require the conduit to be much larger than needed if individual wiring was pulled in, as normally done by electricians.

    Why do you need to pull SER cable in underground conduit?

    What size SER and conduit?
    jft1000's Avatar
    jft1000 Posts: 1, Reputation: 1
    New Member
     
    #3

    Dec 18, 2012, 09:47 AM
    Installing stand by gen. and would like to run 4/0 ser from ATS 50 ft indoors to a 15 ft 2 1/2 in dia. Conduit run from basement to Gen. pad. I would like to strip the length going into conduit and connect to conduit with a 2 hole clamp connector
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #4

    Dec 18, 2012, 10:30 AM
    See NEC 338.12(A)(2):
    You are not permitted to install SER cable underground with or without a raceway.
    For underground installations the cables will need to be listed... (typically THWN)

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search


Check out some similar questions!

Can telephone cable and television cable put in one electrical conduit [ 5 Answers ]

Can telephone cable and television cable put in one electrical conduit?

What size conduit for 4/0 ser [ 3 Answers ]

What size conduit is Min. for 4/0 Ser cable? Is 2" sufficiant? Just from the disconnect to the Crawl Space? I guess what I am asking I have already ran 2" from Disconnect to an 2" LB 36" then a short stub to under the house. Is there enough room to get 4/0 ser in the 2"... I had origianally...

Which to use, SER or Conduit THHN Cu for SE? [ 8 Answers ]

I am renovating a small house and moving the Load Center from the crawlspace to a first floor, center of house location. The service to the house is currently 100Amp but I will upgrade to 125Amp. I am having a Main Breaker installed outside, next to the meter, so I have a disconnect to...

200 amp service 4/0 ser cable in 2" conduit? [ 1 Answers ]

What should I run from my disconnect switch to my panel box inside for my 200 amp service. I have 2" PVC ran from the disconnect to the panel. I thought about using 4/0 SER but then read somewhere that you are not suppose to put it in conduit because of possible temp problems? Is this correct or...

SER Cable [ 1 Answers ]

Is SER cable (0,0,0,2) direct bury, or must it be in conduit?


View more questions Search