    Whirlpool Wiring
    Hi
    I installed a whirlpool tub and I need to connect the pump. I know it requires a dedicated circuit but is almost impossible. I decided to use the washer machine circuit (is the only consumer). Anybody has an idea what would be the risks besides code violation?
    In connection with this: the wire from the main panel to the junction box is an old 12 cupper, but the ground wire is probably 18 or so. Will it be a problem if I connect this with the ground from a different circuit in the house where I have a 12 ground?

    Thank you
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jun 20, 2012, 12:06 PM
    Not recommended mixing ground wires from different circuits.

    The #18 ground I realize came with the older cables.

    This will be protected by a GFI device, which will help protect you, even if there was no ground at all.

    I suggest using the washer circuit, if absolutely necessary.

    Obviously, my strong recommendation is to install a proper circuit.
    visa666's Avatar
    visa666 Posts: 9, Reputation: 1
    New Member
     
    #3

    Jun 20, 2012, 12:34 PM
    Quote Originally Posted by tkrussell View Post
    Not recommended mixing ground wires from different circuits.

    The #18 ground I realize came with the older cables.

    This will be protected by a GFI device, which will help protect you, even if there was no ground at all.

    I suggest using the washer circuit, if absolutely necessary.

    Obviously, my strong recommendation is to install a proper circuit.
    Thanks for answering tkrussell.
    Unless I take down 20 feet of celling that's no way I can run a dedicated circuit.


    One more thing: the manufacture recommends a 15 amps circuit and a 20amps GFCI... how this works?

    Thanks again
    ElectricianMan's Avatar
    ElectricianMan Posts: 5, Reputation: 1
    New Member
     
    #4

    Jun 20, 2012, 01:47 PM
    Quote Originally Posted by visa666 View Post
    Hi
    I installed a whirlpool tub and I need to connect the pump. I know it requires a

    Thank you
    First of all you say that it is nearly impossible to install the wiring . That is not true . It is actually very easy to install a new dedicated circuit to this whirlpool . I know I know , how can you say that when you don't know how my house was built ? But I do know how your house is built . The first thing you should realize is that you're being cheap . The second thing that you should realize is that you're fooling around with electricity and water . Enjoy a nice relaxing soak in the tub knowing that the person who wired it has no idea whether it is going to electrocute somebody . If your house is built on a slab which is the only reason why I could think that it would be difficult to install the dedicated circuit you simply Hire an electrician to cut the sheet rock which is about as difficult to cut as cardboard . All a qualified electrician would have to do is cut the sheet rock above the electrical panel and cut the sheet rock in the bedroom directly above the garage where the panel is usually located . No matter where the panel is located A qualified electrician will simply go inside the house and cut holes in the sheet rock above the panel and go to the second floor if there is one and cut two more holes in the wall to get the wire into the attic . Then you're qualified electrician will find a wall in the home that is contiguous From the first floor to the second floor in the area of the said whirlpool tub . Then the qualified electrician will run the wire down into the first floor and install an outlet . This outlet has to be ground fault circuit interrupter protected and needs to be on a dedicated 20 amp circuit . With the diminished ground that you describe in a fault current situation the ground can burn in half and someone may get electrocuted . An electrician cannot run to another circuit to get the ground wire because this is illegal and stupid . In the case of electricity there are laws for a reason , unlike the tax code . According to the national electrical code you need to run the ground wire all the way back to the main electrical panel should you desire to ground an outlet that is not grounded . Which basically means hire an electrician to just install a new circuit . You cannot have a qualified electrician tap off the washing machine circuit because of the national electrical code but also because the combined load of the motor in the whirlpool tub and the motor inside the washing machine will exceed 80% of the breaker value being 16 A . When you exceed this amount of current the breaker will start to trip and or burn up inside . Don't pay some jacked leg electrician to jury rig your whirlpool tub . And certainly don't do illegal electrical work yourself . Save up the money that you're making at the buy more and pay someone to do it right. Pull an electrical permit and afterwards sit in your whirlpool tub and enjoy a nice relaxing bath with piece of mind knowing that your chances of getting electrocuted have been diminished by about 99% . Link Removed
    visa666's Avatar
    visa666 Posts: 9, Reputation: 1
    New Member
     
    #5

    Jun 20, 2012, 03:24 PM
    Quote Originally Posted by ElectricianMan View Post
    First of all you say that it is nearly impossible to install the wiring . That is not true . It is actually very easy to install a new dedicated circuit to this whirlpool . I know I know , how can you say that when you don't know how my house was built ? But I do know how your house is built . The first thing you should realize is that you're being cheap . The second thing that you should realize is that you're fooling around with electricity and water . Enjoy a nice relaxing soak in the tub knowing that the person who wired it has no idea whether or not it is going to electrocute somebody . If your house is built on a slab which is the only reason why I could think that it would be difficult to install the dedicated circuit you simply Hire an electrician to cut the sheet rock which is about as difficult to cut as cardboard . all a qualified electrician would have to do is cut the sheet rock above the electrical panel and cut the sheet rock in the bedroom directly above the garage where the panel is usually located . No matter where the panel is located A qualified electrician will simply go inside the house and cut holes in the sheet rock above the panel and go to the second floor if there is one and cut two more holes in the wall to get the wire into the attic . Then you're qualified electrician will find a wall in the home that is contiguous From the first floor to the second floor in the area of the said whirlpool tub . Then the qualified electrician will run the wire down into the first floor and install an outlet . This outlet has to be ground fault circuit interrupter protected and needs to be on a dedicated 20 amp circuit . With the diminished ground that you describe in a fault current situation the ground can burn in half and someone may get electrocuted . An electrician cannot run to another circuit to get the ground wire because this is illegal and stupid . In the case of electricity there are laws for a reason , unlike the tax code . According to the national electrical code you need to run the ground wire all the way back to the main electrical panel should you desire to ground an outlet that is not grounded . Which basically means hire an electrician to just go ahead and install a new circuit . You cannot have a qualified electrician tap off the washing machine circuit because of the national electrical code but also because the combined load of the motor in the whirlpool tub and the motor inside the washing machine will exceed 80% of the breaker value being 16 A . when you exceed this amount of current the breaker will start to trip and or burn up inside . Don't pay some jacked leg electrician to jury rig your whirlpool tub . And certainly don't do illegal electrical work yourself . Save up the money that you're making at the buy more and pay someone to do it right. Pull an electrical permit and afterwards sit in your whirlpool tub and enjoy a nice relaxing bath with piece of mind knowing that your chances of getting electrocuted have been diminished by about 99% . Link Removed
    I shouldn’t bother but... you either didn't get the question or you love blogging!
    How is "fishing" wires trough walls accepted by the code? In our area they have to be stapled on the stud every 4 feet? It sounds like a "jacked leg electrician" job
    .
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #6

    Jun 20, 2012, 09:23 PM
    Maybe you should read the code more closely before making comments like that . Stapling is only required "when accessible " and not when pulling a wire through a closed wall. Furthermore, When wire is pulled horizontally through a wall it is only stapled at the boxes.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #7

    Jun 21, 2012, 12:45 PM
    I'm disappointed by many of the above comments...
    Being safe by doing a job correctly is far less expensive than Arc flash burns
    Or electrocution... (Any one have kids?)
    Article 406 in the NEC gives a few options for older wiring that may be difficult
    To replace...
    Article 334, in particular 334.30 defines the requirements for installing NM cable...
    Please correct me with some specific code language but I believe as a homeowner in the United States you have the right to submit for a building permit to wire your house... I did
    (If you do, be careful)

    I understand the difficult economy that has been given to us but let's keep the more important things ahead of saving a few dollars or a few minutes...
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #8

    Jun 23, 2012, 08:04 AM
    HFC, my comments were directed to VISA 666 not you.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #9

    Jun 24, 2012, 06:23 AM
    ma0641, Yes Sir, as were mine... general commentary was to bring up specific
    code sections and quote the article when possible to provide those who visit this site with
    the basis for our comments, we don't make this stuff up!
    I would hope to add some value here as you obviously have... thanks

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Whirlpool wiring [ 1 Answers ]

I have a whirlpool dishwasher that mice chewed numerous wires.My son connected all the wires but two or three.I must have the wiring diagram to finish the wiring.It is not behind the kick panel.No one seems to have it.The model number is GU1100XTLB1.

Whirlpool wiring [ 2 Answers ]

I have a whirlpool dishwasher that mice chewed numerous wires.My son connected all the wires but two or three.I must have the wiring diagram to finish the wiring.It is not behind the kick panel.No one seems to have it.

Whirlpool Wiring [ 4 Answers ]

I am replacing a whirlpool tub that had a 20amp single pole service. The tub I got needs a power input of 220v/16A It has a 1hp pump and a 220v 1.5kw heater out of the control box on the tub is a wire with a Black,Blue and brown (Line,Earth,Neutral). I think I have to replace the single pole with a...

WIring a whirlpool tub [ 1 Answers ]

Hi , I am in the process of installing a whirlpool tub in my bathroom and I need to run a dedicated circuit to it. I have an unused 220 outlet in my garage that I was hoping to split ad run a line to the whirlpool from. The tub pump is rated at 10.5 amps and there is no inline heater . I was trying...

Wiring Whirlpool Tub [ 6 Answers ]

I'm installing a whirlpool tub in my master bedroom. The elctrical requirement is a dedicated circuit for the pump and a circuit for the heater. Both will need to be GFCI protected. I ran a 12/3 cable thinking I can use a double pole 20 A GFCI breaker. However, I have heard it will not work as...


View more questions Search