    Goodman furnace
    I have a Goodman heating/AC furnace model# GMPN080-4.
    The 3 amp fuse keeps blowing as soon as I put it in AC mode and turn everything on. It will run in heating mode but that is it. Any help would be greatly appreciated.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jun 14, 2012, 02:49 AM
    Quote Originally Posted by nuggeth01 View Post
    I have a Goodman heating/AC furnace model# GMPN080-4.
    The 3 amp fuse keeps blowing as soon as i put it in AC mode and turn everything on. It will run in heating mode but that is it. Any help would be greatly appreciated.
    Check the low voltage control wiring going from the furnace to the outside unit. It is possible the wire got cut or shorted out. Just had a low voltage wire going to the outside unit that got cut with a weed whip it also shorted out. Once repaired all worked OK.

    Also make sure to check the low voltage wiring going into the outside unit also. It is possible the wiring shorted inside the unit and OR the contactor/ starter for the fan and compressor could also be defective causing the fuse to blow.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman furnace with 3 blinking lights and furnace has flame roll back [ 7 Answers ]

I have a GMNT-080-4B Some times I get a 3 blink light issue and then when it starts it has a flame roll back. Also I have to change the ignitor every year. Any help would be great

Goodman furnace GMNT080-4 furnace runs good for a while then has to be manually reset [ 5 Answers ]

I have a Goodman GMNT080-4 (90%). I'm having the same problem As Streatherg did back in the Nov 2006 question. I reviewed his article and tried Every thing on there but seems to be doing the same thing. The furnace kicks on for about an hour then locks out and has to be manually reset threw...

Goodman furnace [ 1 Answers ]

I have a goodman furnace about 8 years old model number is gmp100-3. the problem i'am having is it wants to keep running and starts up while blower is going in the winter during running tries to ignite while still running.could you give me some idea what this problem could be.thank you:confused:

Goodman Furnace [ 3 Answers ]

I have a six year old Goodman Furnace that will not kick on or even begin the start up cycle. Last year I replaced the ignitor and checked it out today and looks fine. Any obvious place I should start to determine the issue? Thanks Jim


View more questions Search