    Ejector Pump
    I am building a new basement bathroom and have most of the work completed and passed by the inspector. He is however telling me that the Ejector Pump needs to tie into a 4" soil pipe. Is this Chicago code? I have it tied into the existing 3" stack.

    Thanks

    Joe
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    May 21, 2012, 07:09 PM
    Quote Originally Posted by chicagojoe2001 View Post
    I am building a new basement bathroom and have most of the work completed and passed by the inspector. He is however telling me that the Ejector Pump needs to tie into a 4" soil pipe. Is this Chicago code? I have it tied into the existing 3" stack.

    Thanks

    Joe
    Hi Joe,
    The fixture vent can tie back to any dry vent but the pit vent MUST be dedicated.
    I believe the exception to this is a Saniflow system. Good luck, Tom

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Ejector pump [ 3 Answers ]

Have full bath in basment with ejector pump. (1)Plumber did not install a check valve. Is check valve a Code requirement? (2) After @15 uses ejector pump does not work. Is not having check valve reason to not work? If not, any thoughts about other reasons for pump to not work?

Ejector pump [ 1 Answers ]

Have ejector pump in basement. After being used 10 or 15 times it isn't working. Realized plumber did not install check valve. (1) Should pump have check valve? (2) Is not having a check valve possible cause of it not working/ (3) If not what are other possilbe causes of pump not working?

Is Meyers pentair sewage ejector pump model SR1830 a quality pump? [ 1 Answers ]

Just installed a sewage ejector pump and I'm somewhat concerned about the manufacture. Not seeing very much information about Meyer. I see Zoeller and Little Giant, so I'm wondering if I got a quality systems. Considering all that was required to get the system in I don't want to revisit this for...

Sewage pump/ejector pump [ 2 Answers ]

My sewage/ejector pump sometimes won't shut itself off. It has gradually gotten worse as time goes by. What could be causing this? Any suggestions appreciated.

Ejector Pump? [ 1 Answers ]

I am new to this website, but have read some of the questions and answers and find it helpful. I just had my basement finished and had a bathroom (toilet, shower, sink) installed. They are all connected to the ejector pump pit. We replaced/upgraded the ejector pump the builder left for us as...


View more questions Search