    Pmoloney's Avatar
    Pmoloney Posts: 2, Reputation: 1
    New Member
     
    #1

    May 16, 2012, 06:57 PM
    Condenser fan motor just hums
    Installed new motor and capacitor.checked wiring at contractor 110 both sides still just hums but compressor runs
    Frank Mangrum's Avatar
    Frank Mangrum Posts: 86, Reputation: -3
    Junior Member
     
    #2

    May 19, 2012, 10:57 AM
    Quote Originally Posted by Pmoloney View Post
    Installed new motor and capacitor.checked wiring at contractor 110 both sides still just hums but compressor runs
    To start with check the wiring along with wiring diagram of this motor and capacitor. May I ask why the motor and capacitor was replaced?
    Pmoloney's Avatar
    Pmoloney Posts: 2, Reputation: 1
    New Member
     
    #3

    May 19, 2012, 04:53 PM
    Fan blade hub broke loose from blade causing bearing in motor to go out . Cap recommended with motor? Contactor replaced contacts all eaten up no silver left. Wiring diagram for unit(heil) no longer readable. Think wiring on Contactor wrong but looks right .motor wires browns to capac,yellow to red line volt, black to black.
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #4

    May 19, 2012, 08:09 PM
    Check voltage on each leg of power entering and leaving the contactor together. Not one leg to ground. It takes 240v to make it work.
    Frank Mangrum's Avatar
    Frank Mangrum Posts: 86, Reputation: -3
    Junior Member
     
    #5

    May 20, 2012, 07:38 AM
    Quote Originally Posted by Pmoloney View Post
    Fan blade hub broke loose from blade causing bearing in motor to go out . Cap recommended with motor? Contactor replaced contacts all eaten up no silver left. Wiring diagram for unit(heil) no longer readable. Think wiring on Contactor wrong but looks right .motor wires browns to capac,yellow to red line volt, black to black.
    Most Heil outdoor fan motors have plug on motor leads and use a duel section run capacitor (capacitor with three terminals labeled HERM -FAN -COM ) that runs fan motor and compressor motor. What type of motor (does it have a three wire plug on motor leads?) and run capacitor (does it have two terminals or three terminals?) was used? Does the motor shaft turn freely? How old is this heil unit?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

My fan motor just hums [ 1 Answers ]

My ac fan motor just hums, could it be the thermostat Thermostat is a white-rodgers model 1f56w-444

My fan motor just hums [ 2 Answers ]

Thermostat or fan motor humming only

Condenser fan motor hums [ 4 Answers ]

I have replaced my first capacitor it worked for about a week than the condenser fan motor stop working again. So I had to change out the second capacitor with the condenser fan motor it worked for a day an now the condenser fan motor stop working again but this time it was hot and smoking. Don't...

Trane condenser fan motor to A.O.Smith condenser fan motor [ 2 Answers ]

The Condenser fan motor I removed from a Trane unit had four wires 1 black, 1red, 1brown and . The black wire went directly to #3 on the relay, the red wire went to the capacitor with black wire from #6 on the relay the brown wire went alone to the other side of the capacitor. I purchased...

Fan motor hums [ 2 Answers ]

My Hampton Bay ceiling fan has worked well for 10 years. But now the motor hums and the blades won't turn. This is true for all 3 speeds.


View more questions Search