    Chiller Question must know
    Hello my name is Otis Ward I have a chilled water for laser.In the basement of my eight story building in November, the outdoor weather air temperature was 38 degree/F and it was to cold to run the chiller how can I put enough load on the chiller on order to keep it running?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    May 8, 2012, 11:29 AM
    Quote Originally Posted by otisward View Post
    Hello my name is Otis Ward I have a chilled water for laser.In the basement of my eight story building in November, the outdoor weather air temperature was 38 degree/F and it was to cold to run the chiller how can I put enough load on the chiller on order to keep it running?
    Otis you will need to pick up a heat source. Unless you can find a free one this can get expensive. Sometimes you can use the domestic water supply in the structure (our underground water here stays 55 degrees F or so all year around). Then you use a water to air heat exchanger or better water to water heat exchanger. Sometimes the structure will have enough residual heat from a boiler or furnace and that can also work. It will probably be best for you to contact an engineer close to your location since calculations will need to be made. Good luck.
    Frank Mangrum's Avatar
    Frank Mangrum Posts: 86, Reputation: -3
    Junior Member
     
    #3

    May 19, 2012, 04:45 PM
    Quote Originally Posted by otisward View Post
    Hello my name is Otis Ward I have a chilled water for laser.In the basement of my eight story building in November, the outdoor weather air temperature was 38 degree/F and it was to cold to run the chiller how can I put enough load on the chiller on order to keep it running?
    You can use a low ambient fan motor speed controler on condenser fan motor to maintain higher head pressure which would maintain sufficient head pressure to prevent low suction pressures at low outdoor temperatures. Not very expensive to have installed depending on what size chiller you have.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Chiller pumps [ 1 Answers ]

What are the difference between primay and secondary pumps ?

Chiller loading [ 1 Answers ]

Got this issue on cooling kW at certain ambient temperature. Leaving CHWT=13 deg.C @ 45DegC- Cooling output is 1397.1kW and compressor input is 491.1kW @50DegC - Cooling output is 1080.8 and Compressor is 397.4 Is it not obvious that if temperature rises the load increases? Why is that at...

Who can answer about chiller [ 1 Answers ]

How can I calculate the size for chiller and AHU unit PIPE :) :) ?

Query regarding Chiller [ 2 Answers ]

Dear Sir, We have LG Steam driven Absorption Chiller of 500 Ton with following specs 1) Chilled water flow 302 m3/hr 2) Chilled water Temp 7 to 12 C In these specs, rated or max flow requirement gainst 500 Ton is mentioned. Please tell me 1) What is the minimum flow...


View more questions Search