    Apr 4, 2010, 06:25 AM
    Can I connect a 10 gauge wire to a 12 gauge wire
    I have 20 amp circuit with 12/3 wire and want to attach 10/3 wire to it. Can't this be done?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Apr 4, 2010, 06:29 AM

    Yes, but WHY? Just use the right wire.
    creativerenos's Avatar
    creativerenos Posts: 6, Reputation: 1
    New Member
     
    #3

    Apr 5, 2010, 12:40 PM

    As long as the wire has equal or greater capacity than the breaker, no problem.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Apr 5, 2010, 04:47 PM

    Creative -- (?)

    Would you like to re-phrase that response?

    10 AWG conductors are rated for 30 amps max.

    12 AWG conductors are rated for 20 amps max.

    Yes you may join 10 AWG to 12 AWG, but your breaker size would be limited to 20 Amps.
    stew_1962's Avatar
    stew_1962 Posts: 255, Reputation: 10
    Full Member
     
    #5

    Apr 5, 2010, 07:01 PM

    You can - but some time from now "somebody" might get the wrong idea about the intent at the 10/3 end. Make sure it is DOCUMENTED.

    Only reason to oversize wires (in my mind) would be to prevent a long run/voltage drop scenario - say, a table saw "way out there in the garage...."
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #6

    Apr 5, 2010, 08:11 PM
    Not a good idea. Somebody may see the 10/3 and ASSUME it's a 30 amp circuit, and install a breaker accordingly. Just looking for trouble using 2 different wire sizes.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire service, wire gauge 100 amp [ 9 Answers ]

I'm installing a 100 amp service in the backyard with a separate meter on a pole next to sub-suface power tranasformer. I have a 100 amp meter box on one side of the pole and a 100 amp braker panel with a 100 amp main breaker on the other side. I'm going to place in it a 15-20 amp breaker for gfi...

Is it safe to replacing a lighter gauge wire with a heavier gauge [ 11 Answers ]

Hi all, One of my baseboard heater (240v)'s wire was broken can I replace it with a heavier gauge wire? Also can different gauge ground wires (copper wire) be connected with a wire-nut? IS THIS SAFE TO DO? OR Will this create a fire hazard?

Connecting 12 gauge and 14 gauge wire [ 4 Answers ]

Is it ever acceptable to attach 14 gauge to 12 gauge wire? I have a remodel situation where I have a 20 amp/12 gauge wired circuit powering outlets only. I want to tap off the end-of-run outlet to power an electric-venting skylight. The skylight comes with 14/2 wire. Can I tap off the 20 amp...

Wire gauge [ 19 Answers ]

I need to know the wire gauge to run an above ground water pump. The voltage will be 220 volts. The pump states max. amps 26, and the length of wire run is 70 feet. Thank you. Matt

Connecting 14 gauge wire and 12 gauge wires in the same blue box. [ 2 Answers ]

I am wiring my basement. All the outlets are running off 2 independent 20 amp circuit breakers connected to each other by 12/2 wire. I wanted to run some stubs off my 12/2 outlets. All each stub would do is run to a small light (max 180 watts) and of course a light switch. Since I ran out...


View more questions Search