    Saniflo connection to future vent
    I am in the process of finishing my basement and intend to have a half bath using the saniflo product. The future vent is approximately 15 feet from where the sink and toilet will be located. It is located between the joists. Is this distance a problem? If not, is the anything special I need to consider given the distance?
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    Mar 24, 2012, 03:58 AM
    A Saniflow Installation unit requires two vents, a pit vent andn a fixture vent. I./m guessing you're referring to the fixture vent. This is a dry vent, correct? Nothing draining from above? What's it venting now? You will have to cut a tee in the vent and run it over to pick up the lavatory. So much for the length of the vet run, Your toilet will be wet vented by the lavatory. As I understand it Saniflo now allows the pit vent to vent back to the house system. So you may be able to revent the pit back to the same vent as then fixture vent. Good luck, Tom
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #3

    Mar 24, 2012, 06:49 AM
    Hi guys

    The toilet connects to the saniflo macerator unit via a flexible connector. The lavatory drain connects into the side of the saniflo macerator unit.

    The lavatory vent and the saniflo macerator pump vents connect together and run over to the future vent. This vent must pitch down from the future vent to the lavatory sink vent at about 1/4"pitch pere foot of pipe.

    The saniflo macerator drain must connect into a large gravity drain pipe and needs to pitch from the highest point (at the macerator pump) to the lowest point (large gravity drain pipe) at about 1/4" pitch per foot.

    Fifteen feet is not an excessive distance from the pump so you are all set there.

    The saniflo macerator pump will come with detailed instructions and can even be accessed via their website @

    http://www.saniflo.com/upload/produc...l_sanibest.pdf

    They also make a sanicompact toilet for a half bath installation (not recommended by me, but an option if space is super tight)... sink connects into the side... that requires different venting setup than presented above.

    Good luck!

    Mark
    tzetlan's Avatar
    tzetlan Posts: 2, Reputation: 1
    New Member
     
    #4

    Mar 24, 2012, 07:10 PM
    Thank you both. Mark - One more follow up question. You indicated to pitch the vent pipe from the future vent to the lavatory sink vent at 1/4" per foot. I was slightly incorrect on my measurements so I just want to verify my understanding. The pipe would come out of the future vent and run 19 feet. I would then need to attach a 90 degree elbow and run for another 9 feet. Does this mean that I would pitch it 4.75" on the 9 foot run, turn 90, and pitch it for 2.25" for the next 9 feet? From that point, I would run it straight down toward the sink and pitch the connection from the sink vent to a tee on this pipe?

    Thanks again for your help. I appreciate it!
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #5

    Mar 25, 2012, 04:25 AM
    Yup... you'll need a total pitch of 7" (4.75 for 19 ft run + 2.25 for the 9 ft run) exactly as you figured.

    Then you stated, "From that point, I would run it straight down toward the sink and pitch the connection from the sink vent to a tee on this pipe"... I am unclear here?

    From the point the vent runs straight down into the sink drain you will branch off (at about 42" off the finish floor) and pick up the vent for the macerator pump... be sure to invert (turn upside down) the tee fitting in the vent for the macerator pump.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Saniflo pump vent [ 7 Answers ]

I was told that I could install a 2" dia x 10 foot long pipe with end capped off on Saniplus macerating pump instead of having to vent it through the roof . Is this correct?

Saniflo tank knocks [ 4 Answers ]

I have a saniflo toilet saniplus about 4 years old. When we flush the toilet and the tank starts to fill, it fills Really slowly then it starts like knocking it sounds like its coming from the wall i.e. pipe but when I shut the water valve off the knocking stops .What is going wrong ?

Saniflo [ 4 Answers ]

Saniflo venting [ 17 Answers ]

Hi all, planning to put a saniflo in the basement to handle toilet/sink. The main line is approx 3ft above ground. In MA we need to have a licensed plumber do the install, which is fine. So I found this pipe in the basement, it's labeled FV (future vent I assume). Is this where the vent will...


View more questions Search