    Jamesgao's Avatar
    Jamesgao Posts: 3, Reputation: 1
    New Member
     
    #1

    Feb 26, 2012, 08:43 PM
    Heil fbf100f14a4
    I have a Heil furnace. I found the motor of draft inducer not work properly two month ago. After I took it off and put some machine oil, it worked well. I knew I need to replace a new inducer soon. I ordered a new one with the same model, and replaced it yesterday. The new inducer works well, but it could not automatically light. My Model is FBF100F14A4, series no is NTG3100GFA4. Any help would be appreciated! Thanks!

    James
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #2

    Feb 27, 2012, 07:57 AM
    Does it eventually light? Or never
    Make sure the rubber hose fron inducer motot to pressure switch is tight,and no cracks
    Do you have a led light on control board blinking /coding?
    Jamesgao's Avatar
    Jamesgao Posts: 3, Reputation: 1
    New Member
     
    #3

    Feb 27, 2012, 09:40 AM
    Thank you for your reply. It never lights. There is no led light on the control board. I have tested the hose by put it into a water bottle. I did not find any air out. Do you think it is no air to push the pressure switch. This is a new inducer and run well. If I use a wire to connect the two wire of pressure switch, do you think it should light?

    James
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #4

    Feb 27, 2012, 12:28 PM
    Jumpering the pressure switch (bypassing) is temperary test ,you can do this to conferm if pressure switch is bad.
    Jamesgao's Avatar
    Jamesgao Posts: 3, Reputation: 1
    New Member
     
    #5

    Feb 28, 2012, 09:34 AM
    I tested the pressure switch and it works well. I can not hear the sound of sparking when the inducer running. As usually, after the inducer running 30 seconds, I can hear the sparking sound. Do you think the spark or sensor wrong?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heil furnace keeps going out [ 0 Answers ]

I have a heil model # NULE075AG01 I replaced the ignator a few months back because it was bad, but the new problem is after it runs for a while and heats up the house it shuts off like it should and when it's time to come back on you can hear the blower motor running but there's no heat, I can look...

I have aHeil model #FBF100F14A4 [ 2 Answers ]

My heater will ignite then stay on for about 1-3 minutes then shut off and cycle through the ignition cycle 2-3 more times sometimes longer and eventually stay on. I changed the limit switch and cleared the pressure switch tube of any condensation but it keeps doing ot.

Heil Furnace [ 0 Answers ]

My furnace is giving me the code of the red light flashing three times, the book says this means that the pressure switch is stuck closed or the manual switch is in the off position. I have checked the manual switch and it is in the on position so I'm figuring this means the pressure switch is...


View more questions Search