    What would cause one hot wire (L1) to swell and the other hot wire (L2) to sag.
    When our fridge is plugged in, the voltage becomes unbalanced. Beforehand, L1 and L2 are both 120 VAC to neutral. After plugging in the fridge, L1 goes to 70 VAC and L2 goes to 170 VAC at the breaker box. The fridge appears to be OK because it will operate fine from our garage (on a separate service).
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #2

    Feb 16, 2012, 10:45 AM
    a522,
    The last time I saw what you're describing the neutral or grounded conductor at the connection outside the dwelling where the utility laterals connect to the service cable had come apart...
    Take a good look outside at your point of connection... should be three wires, two of them are insulated and one is bare, even if this connection appears to be good you should consider calling the utility to come and check these connections.

    If it's not outside it could be inside in your panel... but be careful if you move a conductor under load you may get a large ARC... If you can shut off all the breakers in your panel and still see to safely, check the integrity of the neutral conductor connection... it least you could rule out the panel.

    As always if you're not comfortable working in a live panel call an electrician!
    Be Safe
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Feb 16, 2012, 12:55 PM
    Bad service neutral. Call the power company immediately!
    Then if they don't find anything call an electrician.
    This is not a DIY fix.
    a522467's Avatar
    a522467 Posts: 3, Reputation: 1
    New Member
     
    #4

    Feb 17, 2012, 06:48 AM
    Thanks for the advice. The neutral connections were tight, but the direct buried neutral wire from the pole (meter) to the house (breaker box) must be bad underground. We ran a new neutral wire this morning, and it fixed the problem.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Feb 17, 2012, 11:58 AM
    How did you run just a new neutral??
    If you did that was not complaint.
    a522467's Avatar
    a522467 Posts: 3, Reputation: 1
    New Member
     
    #6

    Feb 17, 2012, 12:52 PM
    We just ran it temporarily for troubleshooting purposes. It has since been removed. Now we are making plans to dig a 200' long ditch and run a completely new power feed. We just wanted to make sure that the neutral wire was really the problem first. Our utilities have been called to identify exactly where the phone line, water line, and existing power feed cables are located, before we start digging.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Is hot wire is not a neutral wire or vice versa in single phase two wire AC source? [ 1 Answers ]

I am a little bit confused why in AC single phase 2 wire source is merely classified the 1 wire as hot and other wire as neutral. The hot wire travels the current from the source to the load and going back the current to the source through the neutral wire. I know that in AC circuit, the signal or...

Can I wire a sail switch directly from 120v to the hot wire of a blower motor? [ 13 Answers ]

I ordered a Honeywell model S688A1007 Sail Switch which I intend to wire N.O. to the hot wire on a blower motor (120 volt, 57 watt, 60 Hz, Panasonic FV-20NLF1 WhisperLine 240 CFM In-Line Fan), like a light swith would be wired. No idea about amp draw on this blower. I'm not an electrician and need...

Al wire on old trailer home, 120v on breaker but 50v on hot wire to outlet. [ 2 Answers ]

Al wire on old trailer home, 120v on breaker but 50v on hot wire to outlet.

How can I use an older 3 wire 220 circuit for a 4 wire hot tub [ 6 Answers ]

Can I somehow use an existing 3 wire 220 volt circuit to power a 4 wire hot tub? Running a new 4 wire circuit back to the main panel will be long and difficult. I have nearby access to an old 3 wire sub panel once used for an air conditioner. This original circuit is missng the ground wire.