    To size my wire trough?
    Hello,

    I'm replacing my main panel with a 100 amp breaker alone ( disconnecting means ) and running out of their to my sub panel,
    30 feet away which will supply all the circuits, reason: location wasn't a good place, but needed within 6'
    From outside meter, so I decided to make a sub panel that supplys the house circuits.

    Above the sub panel, I want to put a trough or junction box to bring all the
    Romex's into the closure and then pipe down to the sub panel. My problem is sizing the pipe from
    The trough to the sub panel and sizing the trough. I've been searching the code book and still not
    Sure on what I should do, I don't need it inspected, cause I haven't changed the amp size of the panel
    And kept it 100 Amp panel. I have a 24 slot circuit panel, 2 which are 30 amps, 2 are 20 amps and the
    Rest are 15 amp breakers, I'm rewiring the house with 2-12 w/ground wire conductors besides the 30 amp
    Breakers which are 2-10 w/ground conductors.


    2-#10 wire romex - 2 cables, total wires = 6 Total wires with grounds.
    2-#12 wire romex - 22 cables, total wires = 66 Total wires with grounds.

    72 Total wires, 6 of them are #10's wire size

    My idea to minimize the size of conduit would to put a ground bar in the trough and run an #8 ground in the conduit to the sub-panel,
    So my new total would be: 51 Total wires.

    So my question would be, What size conduit would I need from the Tough to the Sub-Panel and what size Trough will I need?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Feb 17, 2012, 08:32 AM
    You really need to re-think this idea. You have the wrong idea to begin with,

    The main panelboar or cut off switch must be at the "Closest" point to the service entry, not within 5'.

    The 5' requirement is for connecting your Ground to the cold water pipe. That connection must be made within 5' of the metal pipe's entry into the building.

    If you are making this change for purley cosmethic reasons, then do not do it! Also, if the trough is going to be greater than 24 inches, then you must do adjustments for both cable fill and heat.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Size of wiring trough [ 6 Answers ]

I'm unsure of what size wiring trough to use . I'm coming into the trough from the meter pan with 500 MCM (320 amp single phase service) I'll be coming out to two 200 amp service disconnects and using 3/0 wire. An electrician neighbor of mine recommended a 12" X 12" X 48" trough but the...

Wire size & conduit size for 60 am subpanel 150 from source [ 9 Answers ]

Indiana question: I want to install a 60amp subpanel 150 feet from the main panel. This is all exposed runs both inside and out in a commercial envirenement. What gauge and type of copper wire and what size conduit whould I use. How often should insert a junction box in the run. John

Sub Panel AMP Size and Supply Wire Size [ 1 Answers ]

I would like to install a sub panel in my garage I was told to run 6/3 Romex to supply the sub panel and have done so. The run is about 65 feet and I am now wondering after reading this site what is the max I can get for this size wire? I plan to supply a compressor (20 amp) and the garden...


View more questions Search