    Wire Size and Breaker Size
    I am looking at a 125 ft run of cable to feed a branch circuit in an adjoining building. I have lots (490 ft) of left-over #2 copper cable from another project and a 125 Amp Cutler Hammer panel w/main disconnect that I could use. I have in the main house a 200 Amp Cutler Hammer panel.
    --Can I put in a large double-pole breaker in the main house panel to feed this branch circuit?
    --What is the largest breaker I should use in this main house panel for this branch circuit if I use the available #2 copper cable and the 125 amp panel?
    --Is this 125 amp panel OK or should I purchase a different one (if so what rating)?
    Brsmith135's Avatar
    Brsmith135 Posts: 16, Reputation: 1
    New Member
     
    #2

    Jan 21, 2012, 10:21 PM
    Use 125 amp panel. Feed with 80 amp breaker
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Jan 22, 2012, 04:58 AM
    Need to know what type of "#2 copper cable" you have.

    Certain #2 wire is rated 130 amps, that will allow a 125 amp branch breaker to be used.

    Not sure why an 80 amp breaker was suggested.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What size breaker and wire [ 1 Answers ]

What size breaker and wire for a 400 watt mercury vapor light, running it 35 feet, ballast draws 2 amps at 240 volts.

Wire size for 80 amp breaker [ 1 Answers ]

I am installing a 80 amp sub panel and need to know the size of the wire from the main to sub

Wire size wire & circuit breaker do I need for a 15.8 range [ 2 Answers ]

What size circuit breaker & wire size do I need rfor a 15.8 raqnge ?

Wire and Breaker size [ 2 Answers ]

I am installing a steam generator for a steam shower. The unit draws 38 amps. I need a GFCI breaker. The run is 35 feet. What size wire and breaker do I need?


View more questions Search