    Fan does not run
    Intermittenly, the furnace responds to thermostat call for heat but the blower does not come on.
    SeattlePioneer's Avatar
    SeattlePioneer Posts: 97, Reputation: 9
    Junior Member
     
    #2

    Jan 20, 2012, 02:13 PM
    Take the cover off the burner compartment of the furnace. Obtain the make and model of the furnace off the rating plate in the burner compartment and post it here.

    Observe the sequence of events that occurs at the furnace when you turn up the thermostat and post that sequence of events in order and in detail.
    cwizper's Avatar
    cwizper Posts: 2, Reputation: 1
    New Member
     
    #3

    Jan 20, 2012, 02:18 PM
    It's a Nordyne/Miller M3RL080A BW. The problem is not predictable and only happens on occasion. Someone suggested that the problem may be with the fan control relay on the control board; what do you think?
    SeattlePioneer's Avatar
    SeattlePioneer Posts: 97, Reputation: 9
    Junior Member
     
    #4

    Jan 20, 2012, 02:59 PM
    I think that guessing is not a substitute for correct diagnosis of the problem. Also, I predict that the problem will get worse until the motor won't turn on at all.

    Intermittent problems are the bain of furnace repairmen, but usually you don't have to wait around for them to display the problem.

    In your case, I'd take the cover off the burner compartment and fan compartment. Turn the fan wheel by hand and tell me if the fan wheel is turning freely or if it's stiff and hard to turn.

    Turn up the thermostat to 80 degrees so that the thermostat is calling for heat. Push in the door switch so that the furnace starts when you are pushing in the switch.

    Carefully observe and report here the sequence of events that occurs, including the sound of any relays that turn on to energize the fan motor and whether the fan motor starts easily, whether it starts only after humming, whether the motor overheats and gets hot to the touch and any other details you observe.

    Kepp cycling the furnace until you are well acquainted with the series of eventsa that occur when you push in the door switch. Keep cycling the furnace until the fan motor fails to start, and report on any discrepancies in the sequence of events that takes place when the motor fails to turn on.

    You might need to start the furnace twenty or thirty times before the fan motor fails to turn on.
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #5

    Jan 20, 2012, 08:12 PM
    Can you turn the blower to on at the thermostat and the blower runs? If yes you have a control board that is bad. The good thing is you can set your thermostat to heat, set your temp and let your blower run all the time until you get your board replaced. I keep my blower running 24/7/365 for the last few years.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Ceiling fan won't run one swith outlet light and fan? [ 2 Answers ]

I tried to install a new ceiling fan/lignt kit in the place of an old fluorescent light. The (single) light switch won't turn on the ceiling fan or turn it off (the swith has no control at all on fan/light. The switch worked with the old fluorescent light)---the only way I turned it on/turned it...

Compressor and fan run long after fan inside has gone off [ 1 Answers ]

The compressor and fan outside on my heat pump continue to run long after the fan inside has turned off. I have cleaned the relay contacts thinking that they were sticking but it is still running. Could it be the digital thermostat inside?

Wiring a ceiling fan in middle of run, outlet at end of run [ 5 Answers ]

I am wiring a bedroom ceiling fan and just needed someone to help me figure out part of the wiring I'm not sure about. The goal is to have a 2 gang switch control the light and the fan separately. The switch is at the beginning of the run, then the ceiling fan, and then I also have an "always...

New Compressor Run OK. HVAC Fan only run in Heat mode. [ 15 Answers ]

This board is awesome. I have done some reading first on here. Here's my case: Compr runs fine. Fan on HVAC blower inside runs only in Heat mode. Not on Cool. Not even on "FAN-ON" as opposed to FAN-AUTO. Can this be an issue with relay and board within HVAC? Per other thread, it was talking...

Heat pump: fan does not run with fan set to 'on' position [ 3 Answers ]

I have a heat pump system and a programmable thermostat. The system runs fine, in heat or cool mode, with the fan set to 'auto'. It will not run (no fan) in heat or cool mode with the fan setting set to 'on'.


View more questions Search