    Adding a panel to main service
    I have service coming into the home and straight into a cabinet. Inside the cabinet each leg passes through a ct with 200 labeled on it. They then each go in to a lug. Each lug has two slots for incoming and four for outgoing. 3 of the slots on each lug are taken. The wires run to 3 200 amp disconnects and then to my three panels inside the home. I want to add another panel. I know it has to be a 200 amp panel, but want to make sure that it will work. My amp reading on each leg of incoming power is 45 amps. My total running amps on the equipment I am adding to the new panel is 65 amps. Will this work?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Jan 11, 2012, 07:26 PM
    An amp reading is a meaningless indicator of demand load.
    You need a qualified electrician to come and do a demand load calculation. This will determine if you can add capacity to your already huge service.

    I will say, IMO a 600 or 800 amp service is no place for a DIY to be messing.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Jan 12, 2012, 05:44 AM
    Also, the CT cabinet is off limits to anyone other than the utility.

    If you broke seal to gain access to the CT's, the utility will not be pleased.

    Any additions to the electric service must include the utilty to be sure the new panel is metered properly.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Adding another panel from a 200 amp service panel [ 3 Answers ]

Hi everyone, this is my first post. I have a 60 x 100 ft shop that has a 200 amp service fed in from the pole. Well I added a living space in the shop, which is about 720 sq ft. I plan on doing all the wiring myself and need a little advice on what kind of panel I should use? The living quarters...

Adding a bus to a main panel for ground. [ 2 Answers ]

I have recently added on a room to my house. I have a main power supply out side with a two pole 100 amp breaker the neutral and ground are on same bus, the ground continues down tocopper pole in ground. Upstream ihave added alager box to accommodate more poles. The new box has the two hot wires...

Adding sub-panel to Main Panel [ 3 Answers ]

I am currently considering adding an ELECTRIC TANKLESS WATER HEATER. I have a 200 amp (ITE Load Panel G4040ML1200) with 37 of the 40 poles in use. The tankless water heater requires 4- 30amp breakers. My question is... how can I connect a 125 amp sub-panel to the main panel? Your comments are...

Adding a nuetral bus to an old main panel [ 5 Answers ]

Greetings... Can I add a neutral bus to my houses main panel... I have one bus in there now that is for both nuetral and ground... when I go to hookup the neutral from my 220 gfci breaker to that bus I keep tripping the breaker... the spa is a 3 wire 2 hots and a ground... the instructions say to...

Adding New Service Panel [ 1 Answers ]

I have maxed out my existing Service Panel. I want to add a small additional panel approximately 30 feet away in more convenient, permanently unfinished portion of my basement. I have been told in need to run 6 gauge wire for this from my existing panel. Does anyone know if I need to run this...


View more questions Search