    Adding sub-panel to Main Panel
    I am currently considering adding an ELECTRIC TANKLESS WATER HEATER. I have a 200 amp (ITE Load Panel G4040ML1200) with 37 of the 40 poles in use. The tankless water heater requires 4- 30amp breakers. My question is... how can I connect a 125 amp sub-panel to the main panel? Your comments are appreciated. ART H
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Sep 6, 2008, 06:27 AM
    Quote Originally Posted by artholl
    I am currently considering adding an ELECTRIC TANKLESS WATER HEATER.
    OH god, not another one. I bet the seller conveniently forgot to mention that your 200A service will NOT likely support this monster.


    A demand load calculation IS required here. 200 amps will most likely not be enough, and a service upgrade to 320 is very possibly in your future.
    When this thing kicks in full blast it will use up half of the whole service capacity.

    What else in your home is electric?
    artholl's Avatar
    artholl Posts: 2, Reputation: 1
    New Member
     
    #3

    Sep 6, 2008, 07:12 AM
    Hi Standforty man
    I have a oil burner that heats a 1700 sq, ft. condo and feed a hot water tank, plus three room air conditioner, and a washer and dryer, refrigerator, oven, and microwave... in addition to the normal electric circuits. The sellers of the tankless water tanks (Bosch PowerStar AE125 and Seisco RA-28) states that a 200 amp panel is sufficient (? ). I plan to obtain a power load calculation on the main panel.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Sep 6, 2008, 09:17 AM
    Quote Originally Posted by artholl
    The sellers of the tankless water tanks (Bosch PowerStar AE125 and Seisco RA-28) states that a 200 amp panel is sufficient (??).
    I wonder, without knowing your home and it's loads, how they can determine this?

    200 may be sufficient, barely, but the only way to know is math.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Secondary panel from main panel electric [ 2 Answers ]

Can I use a number @2 aluminum ser 4 wires for a 100 amp sub panel?

Adding a nuetral bus to an old main panel [ 5 Answers ]

Greetings... Can I add a neutral bus to my houses main panel... I have one bus in there now that is for both nuetral and ground... when I go to hookup the neutral from my 220 gfci breaker to that bus I keep tripping the breaker... the spa is a 3 wire 2 hots and a ground... the instructions say to...

Breaker size in main panel to support sub panel? [ 7 Answers ]

Hello, I am wiring a sub-panel to the outside of my home (50 feet from main 200 amp box). I ran 3 wire - 6 gauge. What is the largest 2 pole breaker I can put in the main panel to supply the sub-panel. TYPE NM-B 6-3 WITH GROUND 600 VOLTS CIRTEX-I EZ-STRIP (R) PLUS 17:11 2/5/07 SB/RC ...

Adding main electric panel in multi-family house [ 1 Answers ]

Hello, I just but a two-family (two levels) house in Gibbstown, NJ. The house only has one main circuit breaker panel feeding both apartments. My plan is to live in one unit and rent the other unit. Currently the house only has one electric power meter and one circuit breaker box. The meter...

Main Circuit Panel to Branch Panel? [ 1 Answers ]

Hello experts, OK... My Main Load center in my home has a branch circuit connected to a 60 amp breaker. The branch feed wire is a 4awg copper wire. The branch panel is downstairs and it has a 100amp main cutoff breaker installed in it. It feeds the whole downstairs including... (1)...


View more questions Search